H

hoppy

Hi,

i have a job to install an isolator on a new supply! Basically the dno want an isolation switch mounting before they will connect the new supply! The supply is 100 amp 3 phase tncs. Basically I am going to fit a 4 pole isolator! I was just wondering if this will be ok with the dno, as the neutral will be broken after the incoming earth connection. The customer is not clued up on the details an the job is too far away to have a look, it's go on the day and do it! The supply is eventually going to feed 3 separate properties, I was wondering if I may be better fitting three single phase isolator instead, just after a bit of advice from the more experienced guys!

Thanks


craig
 
if they're having 1 phase per property, it makes sense to have 3 separate single phase isolators. otherwise, isolation of 1 property for maintenance is going to knock all 3 out.
 
Hi tel, thanks for the reply, that's what I thought, but the customer was saying they wanted one isolator for the whole installation! This is something I have never done before, ie working with the dno, that's why I was after a bit of advice, the other thing is I thought if the dno put a new supply in then they would automatically fit the isolator after the meters, with their tails connected?
 
How come the supply is at a central point? You’re isolator should be early make, late break for the neutral.
 
They might want a switch fuse, not an isolator.
Your fuses under the size of theirs as they dont want the call outs.

Boydy
 
Thanks for the replies!

Custer defo says they want an isolator, guess I will need to try and get some more info out of the customer! Seems to me that it depends who actually turns up from the dno and how they feel on the day as to what they will require! Seems to be no set requirement!

thanks again!
 
Install 3 DP switch fuses, one for each property!! You don't install a single 3 Phase switch fuse when the supply is being used for 3 separate properties!! If this DNO service head is located in a central or common cupboard or room, then in all likelihood the DNO will be locating the 3 meters for these properties in that common cupboard/room....
 
Looks like I am going to have to tell the customer what is needed then, as clearly the communication is poor with the dno. So 3 double pole 80amp switch fuses appears to be the way forward!

Then when it comes to it I can run swa cables to the new properties!

thanks for the advice!
 
Install 3 DP switch fuses, one for each property!! You don't install a single 3 Phase switch fuse when the supply is being used for 3 separate properties!! If this DNO service head is located in a central or common cupboard or room, then in all likelihood the DNO will be locating the 3 meters for these properties in that common cupboard/room....


OP text reads to me like its a building with tpn supply to receive (applied for) a tp meter.
DNO might not be aware of future plans.

Boydy
 
OP text reads to me like its a building with tpn supply to receive (applied for) a tp meter.
DNO might not be aware of future plans.

Boydy
well then its up to the person ordering the work to make the DNO aware..isn`t it....with any necessarry guidance from the electrical QS...
 
Looks like I am going to have to tell the customer what is needed then, as clearly the communication is poor with the dno. So 3 double pole 80amp switch fuses appears to be the way forward!

Then when it comes to it I can run swa cables to the new properties!

thanks for the advice!
what you find more often than not is the customers ignorance getting in the way....this is when your guidance comes into play....you can liase with the DNO on the customer`s behalf...as no doubt you wont be fobbed of by the stupid bint on the end of the phone...and/or can get through to the right person/s/department/s without all the undue fuss and nonsense..
 
The DNO may well have asked for a TP+N isolator as a single means of isolation for their service head, i doubt it mind. You would still need the DP switch fuses though, as the tails are going to be over 3 meter in length. This is where a Ryefield board comes in handy for multi occpancey properties, i think the smallest is 4 way, which would be just the job if this property also has a landlord supply for say fire alarm, entrance, stairway and landing lighting door entry system and the like!!
 
Yes at the minute there is a brick built cupboard to which the supply is being put to, this is where the isolation points for each of the 3 buildings will be. Buildings not erected yet but plans signed off. Again I am yet to see this, as I have only been described this over a phone call! I believe 2 will be dwellings and the other a workshop!

is there a requirement for the switch fuses to be double pole?
 