Thanks engineer54, may not have explained my self well, the site is basically a plot of land, which is getting 2 houses and a workshop built on it, so 3 totally separate installAtions, no common areas etc. from what has been described to me is a brick shed / cupboard has been built and passed by the dno to house their new 3 phase supply, a phase per property! Hope that makes it a bit more clear, as said never had dealings with dno with regard to this type of job before, this is why I wanted a bit of advice / guidance from more experienced sparks!

OK, with you now!! lol!!


Are you sure that the workshop building won't need a 3 phase supply for any of the equipment that may be required?
 
The customer doesn't think so, but he isn't the brightest star in the sky. I am going to try and get there next week to have a look and a face to face chat!

if it did need a 3 phase supply, what would your advice be on splitting the other 2 properties across 2 phases?
 
They might, see post 5.

Boydy

I'm afraid you've lost me now, unless you're implying that the downstream Fuses will be of the same rating as those in the service head?? We'll just have to trust that the OP (hoppy) uses 60 to 80A fuses in them there Switch Fuses!! lol!!

Not sure if you'll see much of a discrimination between 80A to the 100A fuses anyway!! lol!!
 
The customer doesn't think so, but he isn't the brightest star in the sky. I am going to try and get there next week to have a look and a face to face chat!

if it did need a 3 phase supply, what would your advice be on splitting the other 2 properties across 2 phases?


Easiest way would be to split the phase + N conductors via henley blocks.

Not much you can do as far as balancing the 3 phase supply, but then it's welcome to the real world, where balancing a distribution 3 phase supply is as rare as the Dodo!! lol!!
 
The customer doesn't think so, but he isn't the brightest star in the sky. I am going to try and get there next week to have a look and a face to face chat!

if it did need a 3 phase supply, what would your advice be on splitting the other 2 properties across 2 phases?
Why not have a separate supply into each dwelling and be done with it?
 
Thanks engineer54, that's what I was thinking as no way to balance the phases.

driverman, that would be he easiest way, but the customer has already got everything sorted for the 3 phase supply, so it is what is, I will just have sort it the best i can!
 
thought it was more to do with the gravitational force exerted by the sun.
 
Thanks engineer54, that's what I was thinking as no way to balance the phases.

driverman, that would be he easiest way, but the customer has already got everything sorted for the 3 phase supply, so it is what is, I will just have sort it the best i can!

The meterings going to be fun and games. The supply company will fit just one 3Ph meter if there's a single 3Ph+N isolator. How are the sub mains to be metered?
This is going to develop in to a saga sorry to say.

I wish you luck sorting it out.
 
The meterings going to be fun and games. The supply company will fit just one 3Ph meter if there's a single 3Ph+N isolator. How are the sub mains to be metered?
This is going to develop in to a saga sorry to say.

I wish you luck sorting it out.

Why would you think that?? It's the DNO that is asking for the isolator as far as i'm aware, and know this service head is to supply 3 separate installations. To be honest, i think all that's needed here is the 3 separate switch fuses, but if the DNO want an isolator at the front end, so be it!!
 