Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor goes into the neutral block first then to an earth block that's connected to the incoming cables sheath. My rather unhelpful supervisor told me to "figure it out for myself" today, I think someone was having a bad day...

If the consumer unit is getting swapped out would you run the replacement 16mm main bond to the Neutral block and 10mm supplementary bonding to the earth block on the side of the incomer shown below, gas and water so you would have 3 supplementary bonding cables?

Thanks

1688055092893.png
 
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor goes into the neutral block first then to an earth block that's connected to the incoming cables sheath. My rather unhelpful supervisor told me to "figure it out for myself" today, I think someone was having a bad day...

If the consumer unit is getting swapped out would you run the replacement 16mm main bond to the Neutral block and 10mm supplementary bonding to the earth block on the side of the incomer shown below, gas and water so you would have 3 supplementary bonding cables?

Thanks

View attachment 109121
Phone the Dno and ask them to upgrade.
 
It was TN-S, it is possible earth continuity broke down and it was changed and the existing earth braid was connected into the earth terminal to earth the cable sheath, it doesn't need upgrading it isn't uncommon.
 

Reply to TNCS or TNS earthing arrangement? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
285
Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
524
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock