Please bear with me, iam not an electrician so I hope the following makes sense. I run a mobile seed cleaning unit - basically an 18 tonne lorry with a 60Kva generator powering various 3 phase powered machinery to process wheat and barley on different farms. In the past we have been told at each, worksite to drive one of the lorry wheels onto a 15mm thick alluminium plate connected to the generator to act as an earth. We have now been told not to do this. My question is, if a fault developes will the current now pass through me as i touch the machine before the generators rcd trips or will the fault current go back to the windings of the generator.

hope someone can enlighten me.

many thanks, Neil
 
I suppose in theory if all the electrical equipment is bolted with a good electrical connection to the common chassis, which is earthed back to the star point in the generator and the unit is separate from earth (insulated rubber tyres) then there should be no danger to anyone in contact with earth as there is no path from the general mass of earth back to the generator. If a item of equipment developed an earth fault then the current would flow through the chassis earth and the protection would operate (RCD). As the resistance of the bolted connection would be less than the resistance of you standing on the chassis and say touching the faulty equipment you would be in no danger.
 
Last edited:
Modern tyres have carbon impregnated in the side walls so are not insulated from earth. Industrial flexible hoses often have steel braiding so possible earth paths.
As to the earth plate I personally would carry on using it.
 
I can see what you are saying Tony but with good reliable earth connections between the motors-chassis and back to the generator the resistance back through the tyres would be much greater. The earth plate or a rod would be required if equipment was used away from the unit i.e not directly connected to the unit.
 

OFFICIAL SPONSORS

Back
Top