Center tapped to Earth transformer maybe???I’ve seen a 110v control transformer reading 28v on the neatral to earth and 67 on the other leg. Why would this be?
So it’s an isolating transformer? If it is can these be modified to make the neutral true 0v?The output is probably not earth-referenced, i.e. it is electrically separated / floating. The voltages to earth are not defined and the actual readings on the meter are not very meaningful, giving only a hint at the relative amounts of leakage / capacitance from the two lines. They will probably vary according to different instruments and a low-impedance meter might not show any reading. On a floating circuit what you do not want to see is zero on one leg and the full voltage on the other, as that might indicate a short to earth.
It’s simply just a transformer for a control circuit that runs 2 three phase motors for an extraction system it’s industrial so can’t see any reason why it has to be isolating. I’m don’t know weather I’m being silly hear but I thought with isolating transformer I shouldn’t pick up a voltage to earth? Just between each end of the transformer winding?Simply connect one end of the winding to earth and call it the neutral. Why do you want to change it? Have you considered why it is arranged this way now? Is anything depending on the electrical separation for safe operation?
Interesting but if it was earthed I can’t see the problem from a safety point? With isolating transfers what’s to protect us on the second fault?Well that would be true if there were exactly zero leakage and zero capacitance to earth. But even before you start to run cables from it, the transformer secondary has capacitance to earth, through which a small amount of AC can flow to give a reading on the meter. The more cabling and equipment, the more leakage can flow. It's a ghost voltage if you like that term, that will probably go away if you use a low-impedance tester.
Floating circuits are single-fault tolerant, and can reduce the voltage and leakage in critical places where insulation is challenged. Don't change the configuration simply because you 'like' one wire to be neutral!
Each leg 55v to earthCenter tapped to Earth transformer maybe???