Jako13!: Now study this diagram for the situation where the secondary side is imperfectly isolated from ground/earth by say insulation leakage indicated by the three pure resistors. Assume your voltmeter has a very high resistance (say 50M Ohms) which means it draws only a negligible but not zero current to take a voltage reading.

What would the voltmeter measure when connected between earth and L1, L2, L3 and L4? First though draw a circuit diagram for the upper and then the lower 110V circuits.
 

Attachments

  • imperfectseciso.png
    imperfectseciso.png
    72.6 KB · Views: 54
JAko13! - Could you say a little more about these links? Pictures are helpful. This way the 'EF Brains Trust' can comment further. In the meantime I am confident you will not alter anything. What is the purpose of the panel?

:)
 
But it's not. 28 volts was measured, which is almost certainly not a 'real' voltage.
The wiring diagram of the Tx is visible in the OP pic., and the earth connection doesn't connect to either winding, so it's a screen.
What do you mean " a Screen"?
 
What do you mean " a Screen"?
Copper foil sheet between the primary and secondary windings. The sheet is arranged so that it doesn't form a shorted turn. Used when one winding is wound on top of the other.
The other method of making an isolation transformer is to position the windings side by side with a space between them
 
Copper foil sheet between the primary and secondary windings. The sheet is arranged so that it doesn't form a shorted turn. Used when one winding is wound on top of the other.
The other method of making an isolation transformer is to position the windings side by side with a space between them
So why do we use 110v transformers for electrical safety?
 
It might well be connected to earth at the DC side of some power supply, so really don't go changing it unless you have access to the full schematic and design details!
 
So why do we use 110v transformers for electrical safety?
There are 2 different but related aspects:

One is the danger presented by the secondary voltage itself. So you can easily kill yourself on a 240V isolated supply just but getting both ends of it, and do so without too much more difficulty on 120/110V (as US electrical accidents sadly testify to). Going down to 55-0-55 puts it out of most danger situations, unless very wet (insert joke here...)

The second danger is that of a flashover between the primary and the secondary. One traditional solution is a split-bobbin style of construction so the windings have a mm or so of solid plastic insulation and a cm or so of creapage distance between them. Another solution is to put an earthed screen between the two. This is also an advantage if electrical noise is an issue, as anyone familiar with old valve LW/MW radios will know...

That is, before all broadband modems throwing noise all over the spectrum so folk could wast time on arsebook....
 