Rupert, as you 1st post.join L and E of 1 legin the CU.measurer R1+R2 at each socket. ( only those on that leg will five a reading ) . mark each socket with a wipeavle felt pn with its reading. repeat for other leg. then you can map out the circuit and see where the break, if any, is. options are then to either:
1. reinstate ring, if practicable.
2.convert to 2 x 20A radials.
2.5mm T/E will have a reading of approx 0.02 ohms/meter. (remember to null leads beforehand.).
Thanks for that telectrix that's along the lines of what I was thinking.
The 0.02 ohms that you quote is that R1+R2 ?
Can you point me to a Low Resistance Reading Ohm meter as mine has only 0.1 accuracy and I had noted that when checking for a bridge I would be looking for readings within 0.05 Ohms