a filament lamp will read around 80 ohms cold. still too high for some continuity testers.
 
sounds to me like you have lost your neutral if you have removed the neutral from the board then you will get 230volts on the neutral between the earth and neutral , not a very clever thing to do as you could electricute yourself if you touch it, to test it properly do an r1r2 test to ensure you have good continuity on the circuits then do an r2rn to ensure you have neutral continuity

So even when I remove a neutral from a different circuit in the fuseboard and test between Earth and that neutral the voltage will still be 230v?
 
so the N is dangling and there are 1 or more lights switched on. as the circuit is open circuit at the n END, then you will have 0 volt drop across the load, therefore you will get the line voltage on the N.

Really helpful cheers telectrix, so if there is no load on the circuit (all of the lights are off) will there be any voltage at the neutral?
 
So even when I remove a neutral from a different circuit in the fuseboard and test between Earth and that neutral the voltage will still be 230v?


yes think about it like the lads have said you may not get continuity readings if the light switch is switched on breaker on , lamp in the holder then the 230 volt will run through the circuit back to the neutral bar hence making the circuit , if you disconnect the neutral then it stays positivly charged so you will have 230 volts on the neutral , like i said in my post you need to check the circuits continuity by using the r1r2 , r2 rn formual this will confirm polarity and continuity of the cpc , live and neural conductors
 
sorry mis read your post , dont go removing neutrals from other circuits with the power on you could end zapping your self if all your switches are off then you shouldnt get 230 volt on the neutral thats if you have the correct neutral or if you have a shared neutral you could end up with 230 volts , you could also get a lower voltage reading due to induced voltage
 
This has to be a college question if not this guy is dangerous. To be fair I did get a belt today off a borrowed neutral it was dead until my mate turned another lighting circuit on not the one I was working on and that's how we found it, and I must say it was a painful one. But this building had a periodic done 8 weeks ago and passed, me thinks they used the magic invisible test kit .
 
nuetral has no return path , ie connected and leaving board but disconnected before load
 
I was shocked as well (not literally) and that's what I thought about the polarity but it still doesn't explain why there is no continuity between the Line and Neutral conductors?

why would there be continuity between live and neutral ?
breaker would obviously trip :S
the neutral has no return path and has became live
 
Somebody needs to get someone who is competent to check the neutrals are all correctly connected I think lol
 
Light still switched on ,on circuit and neutral dangling ....

Just touch to earth to see if protective device works
 
He's at board witth circuit on and neutral disconnected , with light switched on somewhere , am I Wong
 