would you prefer a caravan park to be designed completely tt from dno point or tncs up to hook up box and only tt the van's female commando connection on the hook up.?

pros and cons would be good reponses.?
 
what about when you have severall different toilet blocks/ launderette/ stores / amenity blocks coming off local sub stations.? would these building benefit a pme supply.? tncs to hook up boxes.. individual earth pits next to pitch for commando plug.?
 
hi all.. new member need 6 posts to access everything on here.! so thought id post this question to get some different opinions.

would you prefer a caravan park to be designed completely tt from dno point or tncs up to hook up box and only tt the van's female commando connection on the hook up.?

pros and cons would be good reponses.?

Supplies out to permanent buildings such as club house, park shops (and the like), laundry blocks, shower blocks etc ...will benefit from remaining on the DNO's PME park supply.

All distribution cables out to supply caravan pitches will be best suited to an overall TT system, Rodding at each hook-up unit, and linking the rods between hook-up points via the SWA cables armouring. Done properly, you should achieve a stable and very low RA value on each distribution cable or distribution ring....
 