Pg 33 of OSG 5.1 para (ii) refers to isolation for every circuit. For a TT system it states that for every circuit or group of circuits that may need isolating without interrupting the supply to other circuits, the isloating device must switch all LINE conductors ( other than at origin ).

Can someone confirm that a split load ( dual RCD ) CU meets this criteria. Obviously you can isolate 1 half of the board without interrupting the other half but you cannot isolate all LINE conductors for each individual circuit without interrupting another circuit on the same RCD.

Any thoughts greatly appreciated.
 
If you look at the Reg that it refers to, the OSG is not exactly correct IMO.

As far as im concerned, yes, in a TT system, there should be a means of isolating both live conductors, which is the main switch.

On a TT CU change i did for my assessment last year, i wasnt even questioned on it by my assessor.

Sintra is your man for this really.
 
Just looked at the reg and I agree but Reg 537.2.1.1 refers to a TN-C-S or TN-S not requiring isolation of a Neutral conductor if it has a suitably low impedance to earth.

Is it me is this an open ended statement. Where would this stand with a TT system.

It seems open to various interpretations!!
 
It is indeed and this is what makes this job so hard!

The way I see it is that in a domestic situation, a normal cu with a DP main switch meets the requirements.
 
Pg 33 of OSG 5.1 para (ii) refers to isolation for every circuit. For a TT system it states that for every circuit or group of circuits that may need isolating without interrupting the supply to other circuits, the isloating device must switch all LINE conductors ( other than at origin ).

Can someone confirm that a split load ( dual RCD ) CU meets this criteria. Obviously you can isolate 1 half of the board without interrupting the other half but you cannot isolate all LINE conductors for each individual circuit without interrupting another circuit on the same RCD.

Any thoughts greatly appreciated.

Your original quote is wrong - for a TT system all live conductors need to be interruptible, eg a double pole isolator. What the OSG is saying is that if you need to isolate some circuits, say for maintenance, with a TN system then a single pole device is acceptable but with a TT system any isolator that is used for such isolation has to be double pole. However at the origin of the installation in a normal domestic situation it has to be double pole regardless of whether it is TN or TT.

It is not saying that all individual circuits on a TT system need DP isolators, unless you want to be able to regularly switch that individual circuit off. I think the clue is in the word "may" from your quote. If you need to work on a circuit in a TT installation then it may well be that you are switching it off at the DP main switch.
It seems you need a degree in English to interrpret some of these regs :)
 
Last edited by a moderator:
I did mean LIVE conductors otherwise there was no point starting the thread!!! :)

Thanks for clearing that up for me pushrod, been a great help.
 
I read it as "circuit or group of circuits that may have to be isolated WITHOUT interrupting supply to other circuits" not many in domestic properties that cannot be isolated during work. so the isolator or RCD meet regs.

Wish they would write the regs so they make simple sense!!

If you look at page 24, figure 3.2 would be wrong! I suspect one day RCBO's will be the min requirement.
 
Last edited by a moderator:

Reply to TT Isolation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

OSG Pg.40 says: '[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault...
Replies
79
Views
7K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
769
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Customer has a large metal caravan with three phase supply feeding 3 metal Consumer units with split load RCD outlets contained within - all...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock