I guess as we have traditionally considered having correct polarity an essential aspect of an installation. Our plugs are only line-fused, and many switches are line-only, so polarity matters whether TT on TN and so no advantage in safety terms for the board MCBs to be double-pole.

But on a TT system the incoming RCD would be all-pole so there is some protection for high N-E voltage faults even if unlikely.
 
I guess as we have traditionally considered having correct polarity an essential aspect of an installation. Our plugs are only line-fused, and many switches are line-only, so polarity matters whether TT on TN and so no advantage in safety terms for the board MCBs to be double-pole.

But on a TT system the incoming RCD would be all-pole so there is some protection for high N-E voltage faults even if unlikely.


Right- you have the correct polarity. But you have no grantee the neutral will remain at about 0 volts relative to the building's earthing system.
 
Personally I would prefer to see DP or SPSN MCBs. They are much more widely used in mainland Europe where TT is more common. We seem to have a general disinterest in them, perhaps because we are generally pretty consistent about preventing significant N-E potentials at source and would gain little in practice.

We always have DP isolation in all SP+N CU's though as PC1966 points out.
 
Realistically the SP+SN option for RCBO is more useful in terms of allowing N-E faults to be identified and circuit testing performed without much cable removal. but not very common outside of the Wylex/Crabtree ones in the UK it seems.
 
Realistically the SP+SN option for RCBO is more useful in terms of allowing N-E faults to be identified and circuit testing performed without much cable removal. but not very common outside of the Wylex/Crabtree ones in the UK it seems.

Yes it would be a vast improvement if everyone followed suit.

I am annoyed that schneider didn't take the opportunity to include this in the new range of Acti9 PoN boards, when they changed to a neutral busbar and plug in contact instead of flying leads on the RCBO I'm sure they could have included switching of the neutral too.
 
Personally I would prefer to see DP or SPSN MCBs. They are much more widely used in mainland Europe where TT is more common. We seem to have a general disinterest in them, perhaps because we are generally pretty consistent about preventing significant N-E potentials at source and would gain little in practice.

We always have DP isolation in all SP+N CU's though as PC1966 points out.


I've noticed that. Mainland EU always goes DP and SPSN... but the UK seems to have no concern. Do neutrals not break in the UK?
 
Realistically the SP+SN option for RCBO is more useful in terms of allowing N-E faults to be identified and circuit testing performed without much cable removal. but not very common outside of the Wylex/Crabtree ones in the UK it seems.


True, had no considered this.
 
Yes it would be a vast improvement if everyone followed suit.

I am annoyed that schneider didn't take the opportunity to include this in the new range of Acti9 PoN boards, when they changed to a neutral busbar and plug in contact instead of flying leads on the RCBO I'm sure they could have included switching of the neutral too.

Do you have a picture of these new consumer units? Sounds like what we are doing in the US.
 
It's common practice to use a time delayed main switch on TT systems for back up earth fault protection and to protect metal cased DB's, in which case DP or SN RCBO's are essential if RCBO's are being used. Standard RCBO's would not be compliant but are often used.
 
It's common practice to use a time delayed main switch on TT systems for back up earth fault protection and to protect metal cased DB's, in which case DP or SN RCBO's are essential if RCBO's are being used. Standard RCBO's would not be compliant but are often used.
Your point about the time delay is valid as a neutral to earth fault will disconnect the main time delay rcd but there’s actually no requirement for the time delay rcd in most domestic installations unless it maybe supplies a distribution circuit , in which case I’d use a dual rcd CU, as DP rcbos can be hard to come by.
 
Last edited:
There no requirement to switch or disconnect the neutral in TN or TT arrangements during fault conditions except for those laid out in part 7. There is a need to be able to isolate the neutral on TT arrangements but this is done by incorporating a 4 pole main switch disconnector in the DB or as what’s required anyway for single phase installations by use of ordinary persons , a DP switch is used regardless of the earthing arrangement.
Rcbos do not have to be DP on TT arrangements unless required to be by the extra requirements laid out in part7.
My post concerned where a time delayed RCD is used as a main switch which you appear to have overlooked.
In that circumstance an earth fault on a final circuit will operate a SP RCBO but the N will not be disconnected probably resulting in the RCD main switch also operating, disconnecting the entire installation. That would be non compliant because division of circuits and circuit protection must be designed for minimum disruption in the event of a single fault.
The only way to prevent that is to fit RCBO's which disconnect the N.
So the installation of SP RCBO's where a T/D RCD main switch is used to protect the metal cased DB is non-compliant.
 
My post concerned where a time delayed RCD is used as a main switch which you appear to have overlooked.
In that circumstance an earth fault on a final circuit will operate a SP RCBO but the N will not be disconnected probably resulting in the RCD main switch also operating, disconnecting the entire installation. That would be non compliant because division of circuits and circuit protection must be designed for minimum disruption in the event of a single fault.
The only way to prevent that is to fit RCBO's which disconnect the N.
So the installation of SP RCBO's where a T/D RCD main switch is used to protect the metal cased DB is non-compliant.
Yeah I deleted the first part of the post as I realised I had misunderstood what you were saying.
 
In main land Europe it is a requirement that on activation the phase and neutral are at least 3mm apart, UK RCBO's with the fly lead do not conform to that requirement and dual pole RCBO's or MCB's have to be used on one RCD, also in France a maximum of eight MCB allowed on one RCD, not sure, but I think Germany is the same.

The main reason for the S type RCD in France is to prevent the customer from using more power that the tariff they pay for, cynical me. :innocent:
 
The French Disconjoncteur de branchement do, if you go beyond your payed for tariff they trip out, the new Linkey meters are even more sensitive and have less head room that the previous Disconjoncteur.
 
How is that possible? I thought RCDs did not respond to over current.

RCD is a term which covers a group of similar devices.
RCCB (residual current circuit breaker) works only on residual current and is what is often referred to as an RCD
RCBO (residual current breaker with overcurrent protection) combines residual current and overcurrent operation, often described as an MCB and RCD combined.
SRCD (socket outlet incorporating residual current device) does what it says on the tin (similar to a USA GFCI outlet but does not provide any protection for outgoing cables which I believe they do in the USA)

There are others, but I can remeber all the acronyms or what the stand for, CBR, RCM spring to mind.

All of them are RCDs,
 
RCD is a term which covers a group of similar devices.
RCCB (residual current circuit breaker) works only on residual current and is what is often referred to as an RCD
RCBO (residual current breaker with overcurrent protection) combines residual current and overcurrent operation, often described as an MCB and RCD combined.
SRCD (socket outlet incorporating residual current device) does what it says on the tin (similar to a USA GFCI outlet but does not provide any protection for outgoing cables which I believe they do in the USA)

There are others, but I can remeber all the acronyms or what the stand for, CBR, RCM spring to mind.

All of them are RCDs,

That clears it up a bit more. When I think of RCD I only think of the literal differential device.

In the US we refer to them as GFCI breakers (5ma) or equipment ground fault breakers (30ma).
 

Reply to TT Supply MCBs in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock