Hi all, :confused:

Ive been to look at a project with a customer this evening. He is looking to put a 100A SPN supply into a remote barn location. He has had Western power out to look at the options, they have advised him they can pull a supply off a overhead line to give him a SPN 100A head.

The problem is that this is 415(ish) meters away from the Barn.

Now this isn't my usual bag, so sorry for the ignorance - and the books are not with me this evening, but I believe the options are as follows:

  • Put a LV TT submain to the Barn, via a trench, which would be a massive cable due to VD.
  • Get western power / others to install a HV radial from the overhead line to a small HV-LV transformer at the Barn. Reducing the size of cable and possibly the project cost?

Im sure I have overlooked some other options, but this one I cant get out of my head.

If anyone has done a project similar id be very interested to hear about it.

Regards all....
 
Hi all, :confused:

Ive been to look at a project with a customer this evening. He is looking to put a 100A SPN supply into a remote barn location. He has had Western power out to look at the options, they have advised him they can pull a supply off a overhead line to give him a SPN 100A head.

The problem is that this is 415(ish) meters away from the Barn.

Now this isn't my usual bag, so sorry for the ignorance - and the books are not with me this evening, but I believe the options are as follows:

  • Put a LV TT submain to the Barn, via a trench, which would be a massive cable due to VD.
  • Get western power / others to install a HV radial from the overhead line to a small HV-LV transformer at the Barn. Reducing the size of cable and possibly the project cost?

Im sure I have overlooked some other options, but this one I cant get out of my head.

If anyone has done a project similar id be very interested to hear about it.

Regards all....
how far away Is an existing supply to pick up from?
 
Theres a TPN supply in a a barn near the over head head lines (450m ish) Not sure of condition or capacity
and the overhead line transformer and suggested position of meter enclosure by W.P is 415m
 
We recently did a job where UKPN 'moved' their supply from a cabinet at the bottom of the clients field, to the house itself. A distance of around 350m. The transformer stayed in the original position - at the bottom of the field. Builder did ground works for them. Cost around £16k
 
Thanks mattG! I suspected that might be the case. I wonder the size and type of cable used for the move. I can't help but think the viability of the project goes out the window with it die to cost and cable size.

Bigspark17 - I was thinking more of UKPN trenching a HV supply to the barn, not sure of the requirements of this however.
 
Have a look at the price for the cable first , before giving it up as a bad job .
Almost always you are far cheaper gettting the DNO just on to the property and then looking at the rest of the run yourself.
We have one at the moment for a isolated new build on one of the estates that we look after , the run is 550m from the nearest source and a 2c 120mm ,just cost us £6149 + the dreaded . Now I know that is not great , but it is better than the £ 78000 + vat from the DNO !
 
Have a look at the price for the cable first , before giving it up as a bad job .
Almost always you are far cheaper gettting the DNO just on to the property and then looking at the rest of the run yourself.
We have one at the moment for a isolated new build on one of the estates that we look after , the run is 550m from the nearest source and a 2c 120mm ,just cost us £6149 + the dreaded . Now I know that is not great , but it is better than the £ 78000 + vat from the DNO !


Thanks fir the input JD4600! Can i ask what calc's you done for the volt drop, when i done some very basic calc's i was getting a 4x120c in parallel to compensate for the VD. I was using a load of 80A (rough guide) and a run of 415m buried in soil at 20'c.

Thanks for the help so far.
 
Thanks fir the input JD4600! Can i ask what calc's you done for the volt drop, when i done some very basic calc's i was getting a 4x120c in parallel to compensate for the VD. I was using a load of 80A (rough guide) and a run of 415m buried in soil at 20'c.

Thanks for the help so far.


Multicore 90°C Armoured Thermosetting Insulated Cables

Tables Apply to: H6942XL, H6943XL, H6944XL, H6945XL, Tuff Sheath,
Voltage: 230V
Load:18.4kW / 80A
Length:415m
Method of Installation:Direct in ground or in ducting in ground
Cable Size: 185mm²

Looks cheaper depending on over current protective device

doncaster cable web calculator

gaz
 
Last edited:

Reply to TT Supply to Barn - LONG distance - help(?) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
734
Guys in a solar PV plant room I have a single phase LV board for power and lighting. This is fed via 2 phases off a solar inverter through a 415 >...
Replies
20
Views
2K
We have recently purchased a home in TX built in the 1920s, and the wiring is an assortment of multiple wiring events. There aren't any local...
Replies
2
Views
2K
I need to augment the underground supply to remote workshops at my own house. I’m struggling to understand the practical implications of voltage...
Replies
11
Views
2K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock