I kind of gave up on them to be honest. Needed to get this job finished before Xmas- Client is getting ****ed off and I need paying!!!
Didn't have much choice, no earth at all!!! I thought putting a rod in was my best option tried contacting DNO but couldn't get a decent response.
I kind of gave up on them to be honest. Needed to get this job finished before Xmas- Client is getting ****ed off and I need paying!!!
Who said I'm giving up on getting this sorted??? I'm well aware of my 'duty of care' hence why I'm trying to get other people's opinions! I will try the DNO again, they're just not that helpful!
It makes a difference because this area is where all the old building rubble is going to be. The further away from building walls the better!!
So WHY have you had to TT this previously TN-S property?? And why didn't the DNO give you a PME connection if it was they're earth provision that failed??
and if it is the DNO earth thats failed.....why didn`t get them to sort out their earthing arrangements that were being used and as such their responsibility rather than go down this route.......or no doubt the DNO lass on the end of the phone told him to rod it....or else..lol..Well i'm assuming that the TN-S earth has failed on the DNO side, i hope so, or the OP is a fool!! lol!!
If you have an 8 foot rod that's only giving you 160+plus ohms in wet sodden conditions, then either the soil type in that area is naff, or your driving the rod through rubble and the like. Your rod position isn't right next to the house outside wall by any chance is it??
You have 2 choices really, 1) Try another rod position in a different area of the property, and at least a metre and a half or so away from any building walls. 2) leave it as it is, and install a S type 100 mA as your main CU switch/isolator.
You could also try as others have suggested add another 1.2m extension to the existing rod and see what that gives you, but as it is, standing at 8 feet, and only giving 160 ohms, i can't see it making much of a difference to be honest!!
The NICEIC don't make the rules thankfully, so ignore any such figures they may be putting forward. A 100 ohm Ra TT system is just as useless as the BS7671 numbty figure of 200 ohm's...