Line and neutral in a single phase installation ................................if you have a load (amps) going down the line they return on the neutral ......ok
You have a Ring final circuit with a load on it ..........so we flow down the Line and back through the neutral ....................still ok
You have a faulty light circuit which is tripping the RCD ..................isolating the breaker still trips the RCD, but when you disconnect the neutral it says in .................... still there
Now because your neutrals are commended at the board your getting the returns from your other circuits back to the neutral bar ...........remember the RFC. well when you connect your neutral from that light circuit into that bar .........you back feeding from the neutral bar into that light circuit, where there is a fault and causing the inbalance, that is causing the RCD to trip ......