hi i was doin a minor works 2day on a light circuit on a tt system i couldnt get a reading for Zs cos me metre tripped out to determin Zs do i mesure Ze witch wos 38.8 and me R1 + R2 wos 0.61 = 39.41 this dont seem rite to me cos the tapulated value for a 6A breaker is 7.67 any help would be great cheers ;-)
 
Thats fine, maz value would be 1667ohms for your 50v touch voltage. Hence the need for an rcd on tt systems.
 
so im right by recording 39.41 for Zs aslong as theres an rcd in place if not id hav to put somethin the remarks collem sugesting action required?
 
Have a look at table 41.5 page 50 of BRB and reg 411.5

If there is no rcd for a socket circuit on a tt i use code 1 and for others i use a code 2 and if only one rcd is used for all circuits in a property i use code 4

I normally record the value i see although i beleive it is ok to record less than 1667

A value of 1667 is only ok if an rcd is used
 
Last edited by a moderator:
im this case thn the rcd used was a 100A main switch with a 30mA trip so would state in the collem tht requires improvement
 
this is rght has to be less than 150ohms for ze thats why you ave to use a 100m/a time delay rcd
 
Ze has to be less than 1667 ohms.

Although anything over 200 is regarded as unstable.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TT sysyems
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
iceman,
Last reply from
iceman,
Replies
8
Views
1,581

Advert

Back
Top