Yes I agree Ze & RCD testing first thing if good maybe supply transformer one pole away. I did have a brief look at it and imo, it's seen better days.
I might just earth it to a pylon or put in a 100A main switch in place of RCD and see if mcb trips.
What the ----!?

What's a Za? Nothing listed in the BGB?
 
Teto, have a think about what you are telling us.

How does an RCD work?

If you improve the Ra, is the RCD more, or less likely to trip?

I suspect that you have fixated yourself on the earthing system being at fault here, when in fact, it may be more than likely that the RCD is either,

A. Doing it's job and detecting a fault.
B. Faulty.

Chris
 
yes i agree ze & rcd testing first thing if good maybe supply transformer one pole away. I did have a brief look at it and imo, it's seen better days.
I might just earth it to a pylon or put in a 100a main switch in place of rcd and see if mcb trips.

omfg.................................................
 
Now don't knock the pylon idea,i did some piling work with Balfour Beatty years ago on the grid and even ENG54 would be impressed with the depths we got CF augering! :dizzy2:
 
Teto,

1. It cant be the the supply transformer mate, it before the RCD!!
2. It cant be the Earth spike mate, is the RCD is tripping which means you have an earth or connection to it somewhere!
3. you said it happens when you have a higher load which presumably is the tranny! Therefore i would try changing the tranny. They are invariably the problem as they are chucked about.

Are your sure its the RCD tripping? i ask only because you said it trips with higher loads. Silly question and its not meant to be sarcastic but i presume you know the difference?

At the risk of repeating everyone elses posts and if you can find someone to show you how to use your tester, please test the Ze, Zs and the RCD and post the results. One of us will be able to tell from that.

Dont guess at things mate it makes you look really daft when youve tried three different things and it still wont work. Mechanics do this and they are idiots!
 

Mechanics do this and they are idiots!

If they happen on that comment,I can see an expensive long drawn out MOT on the horizon
:yes: lol
 
Success! Did some testing Ze (Ra) 112.4 ohms RCD tested good however the test button did not trip it out. Changed cu for new and sunk a 5/8th rod all good and Ze down to 16.8 which is high but lower than 21 in osg. Thanks for all your comments and suggestions.
 
I think I'm going to bang my head on my desk.

I'll 2nd that (or is it 3rd)

- - - Updated - - -

Success! Did some testing Ze (Ra) 112.4 ohms RCD tested good however the test button did not trip it out. Changed cu for new and sunk a 5/8th rod all good and Ze down to 16.8 which is high but lower than 21 in osg. Thanks for all your comments and suggestions.


WHY?????
 