i find the whole " which size tails do we use ?" debate a bit catch 22.
unless you know for sure what size fuse is in the dno cut-out its hard to make that decision correctly.
and you cant do that without cutting seals , removing carrier , etc , etc.
;-)
i'm definately in the pull fuse camp lol.
deliberate mistake methinks....To be fair, 2.2.3 does state a minimum of 25mm. but then goes on to reference 1.3 where this is not the case.
In my opinion this is irresponsible.
I think the OSG is a poor publication and following 7671 is a far better method.
I did not buy the latest version until the scheme assessor would not pass me without it. £20 wasted.
In the OP's case Table 4D5 applies just as it does to the rest of the installation.
well its like owt isn`t it eng....Though probably in the majority of cases where domestic installations are concerned it wouldn't particularly matter much what size the tails are (16/25mm), ...It could make quite a substantial difference in some commercial/ industrial situations as well as in the odd domestic. The tails and/or mains/sub-main cables, will not only be providing power for that installation (or section of installation) but also acting as a limiting/restricting factor for the fault currents that can flow in that cable/installation. So in effect, over sizing these cables, can then become a problem. The closer to the distribution Transformer, the more a one size fit's all and bigger means better is not the route to take!! lol!!
These OSG's seemed to be aimed around the domestic/light commercial arena rather than towards the rest of the industry...
well its like owt isn`t it eng....
what happened to good old fashioned common sense eh?....like askin the client and using your own intuition to decide the best course of action regards tails.....
look, how many....say 2 bed houses are gonna get anyware near 60A for a start?....
If your tails are 3m or less in length, protection for the tails is provided by the protective devices in your CU.
The CPDs in the CU, provide protection in the same manner that a 13A plug top fuse provides protection for the cables of an unfused spur from an RFC.You've said this on another thread as well. Do you really believe this? In many normal installations, the sum of the ratings of the final circuit overcurrent protective devices is significantly more than the rating of the DNOs fuse and the tails, so how can they be protecting the tails?
And if the rating of the supplier's fuse is not relevant, why is it required to be noted on an EICR or EIC?
The CPDs in the CU, provide protection in the same manner that a 13A plug top fuse provides protection for the cables of an unfused spur from an RFC.
If the DNO's allow their fuses to provide protection for the tails, why do they stipulate a maximum length of 3m?