Please think about question 1 in your mind before reading question 2.

Question 1.
If an annex to a building contains a gas meter and CU (fed via a sub main from the main building) then is the bonding required to go back the the earthiing terminal at the local CU or the earthing terminal in the main building?


Question 2.
If the gas meter in the annex feeds the main building as well as the annex then. Same question ( is the bonding required to go back the the earthiing terminal at the local CU or the earthing terminal in the main building?)
 
I would have thought it should go back to the MET of the main incoming supply as it is thepath of least resistance given cable size and there will be less connections to fail? but having said that would it be a good idea to have a secoundry bond to the annex CU?
I'm new to the game so just giving my thoughts.
Paul
 
Back to the MET on the main board, otherwise you're relying on the earth that feeds the CU in the annex which might not be as big as the bond.
 
Please think about question 1 in your mind before reading question 2.

Question 1.
If an annex to a building contains a gas meter and CU (fed via a sub main from the main building) then is the bonding required to go back the the earthiing terminal at the local CU or the earthing terminal in the main building?


Question 2.
If the gas meter in the annex feeds the main building as well as the annex then. Same question ( is the bonding required to go back the the earthiing terminal at the local CU or the earthing terminal in the main building?)

its a tricky one this especially in in schools etc.

i normally bond the MAIN gas meter and MAIN incoming services as required back to MET in apprpriate cable size ( normally largeish if its a 400amp supply )

i also treat any annexes or outbuildings with their own dist. board and additional extranaeous conductive parts such as heating pipe work, gas supply pipes, secondary gas meters etc. as an equipotential 'zone' and bond locally back to the associated local DB.
 
Please think about question 1 in your mind before reading question 2.

Question 1.
If an annex to a building contains a gas meter and CU (fed via a sub main from the main building) then is the bonding required to go back the the earthiing terminal at the local CU or the earthing terminal in the main building?




Question 2.
If the gas meter in the annex feeds the main building as well as the annex then. Same question ( is the bonding required to go back the the earthiing terminal at the local CU or the earthing terminal in the main building?)


What type of gas pipe is it from meter in the annex to the main building?

Are there any gas appliances within the annex?
 
Surely the annexe gas equipment would be treated as any extraneous conductive parts woiuld be, i.e. if continuity back to main db is less than 1667ohms, preferably under 200ohms then all's ok there? Or should I just crawl back under my duvet and keep quiet?
 
just got this- snags solutions nic eic Re emerging metallic pipework may need to be connected to the main earthing terminal (met) at the point which it re-emerges. Aswell as the point of entry to the building, reg 544.1.2

Also if meter is external (connection should be made to the consumers hard metal work beforeany point of entry to the building)

hope so
 
Last edited by a moderator:
Also if meter is external (connection should be made to the consumers hard metal work beforeany point of entry to the building)
The actual quote is "Where practical the connection shall be made within 600mm of the meter outlet union or AT the point of entry to the building if the meter is external" and since you can't actually bond inside the wall, to me that means immediately after the point of entry. ie no need to drill holes through the wall.




On the general front,

Thanks everybody, that's given me food for thought.
 
Last edited by a moderator:
Is that regs or nic, and 17 th. The nic interprets the regs diffently. Only writing what i read curtousy of the nic.
 
Think of it as a block of high raised flats where you have the utility supply entering the building and terminating in a Lucy box or similar. From there it will feed main switches which feed the sub mains in the riser and splits at each floor. You would not drop a earth bond cable down 22 floors for each flat, 6 per floor to the MET on the ground floor just because that where the service entry point is to the building. The SWA cable armour of the sub-main would be used as the main earth for bonding and that would be for 6x22 flats= 132 flats.

Similarly if you used MICC (Pyro) you would not run a separate earth as long as it is a 'sub-main' and not a final circuit.

So to answer your question the 'sub-main' (an extension of the main) also acts as an 'earth main' In other words the sub mains earth is your main earth to that building which you can bond to.

Hope that makes sense.

Ex Electricity Board Electrical Engineer
 
Main Building - Bond main gas pipe to MET
Annexe - Bond Annexe gas pipe to Annex Dist board
 
Tacon, FYI, my reprint was directly formn the 17th , section 544.1.2 as you rightly refered us to.

mazdaman, A very good point.

From the NIC: If the annex were a seperate building, then the sub-main would be terminated with a BUilding Main Earth (BME) to which the bonding would be attached. Then (as rightly quoted by somebody eqarlier) where the buried gas pipe re-emerged into the main building it would have to be bonded again to the MET.
 