Reading posts about TT systems and earth rods lately,I,ve noticed that sometimes people have problems getting a low enough measurement,now I realise that not everyone is familiar with ufer earths so I thought I,d mention them,basically they were developed for the us military by a man named ufer who came up with the idea of encasing an earth rod in concrete when soil conditions were poor,is dry stoney soils.concrete is more conductive than these types of soil due to the higher alkalinity of the cement,also it tends to retain moisture for longer than the surrounding soil.the original ufer,s were just a hole about six inches diameter dug to the depth of the rod and filled with concrete,the rod being pushed into the middle and allowed to harden,later on the copper rod was replaced with a steel one after it was discovered that over a period of time the alkalinity of the concrete caused the copper to flake.Nowadays ufers are normally made by making use of the rebar in large concrete floors,the rebar being either double tied or welded together.However going back to the origin al method of digging a hole and encasing a standard rod in concrete,this may help some people if they find they are unable to drive a rod to a greater depth due to ground conditions.just thought I'd give this a mention.
 
Saw that some years ago when I worked on airfields never gave it notice until you mentioned it well done for the reminder
 
Reading posts about TT systems and earth rods lately,I,ve noticed that sometimes people have problems getting a low enough measurement,now I realise that not everyone is familiar with ufer earths so I thought I,d mention them,basically they were developed for the us military by a man named ufer who came up with the idea of encasing an earth rod in concrete when soil conditions were poor,is dry stoney soils.concrete is more conductive than these types of soil due to the higher alkalinity of the cement,also it tends to retain moisture for longer than the surrounding soil.the original ufer,s were just a hole about six inches diameter dug to the depth of the rod and filled with concrete,the rod being pushed into the middle and allowed to harden,later on the copper rod was replaced with a steel one after it was discovered that over a period of time the alkalinity of the concrete caused the copper to flake.Nowadays ufers are normally made by making use of the rebar in large concrete floors,the rebar being either double tied or welded together.However going back to the origin al method of digging a hole and encasing a standard rod in concrete,this may help some people if they find they are unable to drive a rod to a greater depth due to ground conditions.just thought I'd give this a mention.

IF only it was that easy.... Ufer earthing only really works well when formed from large area foundations, you'll not see much of a an improvement using normal concrete on a single point rod, not unless you go deep which in most cases you can't.... I have had some success adding carbon granules to a cement mix, so you could try that approx.

Also, another problem comes from drilling/forming that hole that you can fill with concrete, ...you could excavate a trench some three metres long and 1 m plus deep, fill the base of that with concrete and drop the rod into that. Even then, a far better solution would be to use ''Marconite'' a conductive mortar/concrete or ''Bentonite'', a moisture retaining clay ...

For those that do a lot of TT systems, a good idea would be to purchase a petrol engined post hole drill and extend the the drill bit by half a metre or so. Drill the hole, fill with Marconite or Bentonite and drive the rod into the base of the hole ( Minimum 2 rod lengths ''2.4 m''). The top section would then provide a better contact with the surrounding soil (and better Ra values) in most weather conditions, that would otherwise not normally be the case.
 
Last edited by a moderator:
Most of the switchroom’s I’ve had dealings with had Ufer earthing along with bonding to the plants structural steelwork. The effective area of the earth could cover several acres. Due to this the MV and LV earths could be linked via a common MET. The requirement for direct connection is <2Ώ on the LV.

We had a number of small MV switching stations (about the size of a garden shed) they each had copper lattice earth mats.
 
the original ufer,s were just a hole about six inches diameter dug to the depth of the rod and filled with concrete,the rod being pushed into the middle and allowed to harden,later on the copper rod was replaced with a steel one after it was discovered that over a period of time the alkalinity of the concrete caused the copper to flake.
It's not really an Ufer earth because there's no concrete involved but we've successfully used the steel sleeving of odex drilled boreholes to get a decent earth impedance on remote installations. It's kind satisfying to get sub 1ohm in dessert conditions.
 
Used polymers including bentonite on grab-excavated and augered piles to 40 metres in Israel,often wondered what Ra readings would have been but had no dedicated tester...just 2 litres of pineapple juice and flaky ears...
 