15.65A so its right on the limit they usually say 16A max...

But just read op again and its on a 13A fcu?? This needs more than a quick fix tel...
nowt i can do about that. all tiled in and no way of separating the circuits. however, it's never blown the 13A fuse in the FCU.
 
i'll try dissing 1 underfloor sensor and see how it goes. these sensors are not a straightforward open/closed. so davesparks post has made me think.
 
Correct.... If you check them on ohms youll see....

Theres a setting on the screen somewhere where you can select air temp youll want it on that anyway
 
if i can, i'll select air temp.customer is loaded so sod the leccy bill. it's a warmup tempo stat.
 
I went to one a while ago and the 13a fcu was pulling 20a, i was called out because it was getting warm and discoloured. why do people not think about things before they install. But back to the problem ... if the stat accepts temp as well as probe , use 1 sensor and air temp.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
Supporter
~
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
UFH brain teaser. think i know but......
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
telectrix,
Last reply from
Pauls0212,
Replies
24
Views
1,910

Advert