Morning all, nipped over from The tiling forum to run a question by you regarding electric ufh, so I'm happy to install the mat and run a continuity test before leveling over and laying tiles, a registered electrician is then usually sourced by my customers to connect up and sort the power out ...but my question is, is it ok for a 9sqm 200watt mat to be wired up to a spur nicked off a socket run or should it have its own feed direct from fuse box and whilst we're on the subject out of interest what would the maximum size 200w mat this is ok to do?

Note; I am not getting involved with messing with any electrics its just something ive witnessed recently and would like peace of mind for my customer it has been done correctly.. Thanks all..
 
200w/sqm = 1800 w
That load is ok to take off a fused spur as you describe..
But, what needs to be checked is that the socket circuit that you propose to spur off is actually ok..- correct size cable, fuse/mcb, RCD protection..
If everything is ok with that circuit then yes just spur out from an existing socket to a fused outlet
 
Last edited:
Also, as well as testing the resistance of the ufh to make sure there is continuity, an ‘insulation resistance’ test needs to be done from the ufh LN to the ufh earth, this is something that usually goes untested by non sparky trades.. due to specialist kit being needed
 
TBH it would be a worthwhile investment if you're doing this sort of installation quite often to invest in a cheap and basic tester to do some testing before you install the mat and once you've finished tiling.

This way you can confirm the mat works from the factory and was not damaged when you did the tiling.

All you would need then is your sparky mate to test, connect and certify as you're doing now comfortable in the knowledge that the UFH will work.

We know how expensive things can get when a UFH system doesn't work.

Something like this: Electrical Insulation Tester - Electrical Cable Insulation Test Meter - https://www.test-meter.co.uk/electrical-insulation-tester/
 
I have no electrical training or knowledge but ive got a multi meter, no idea what the different settings on it are for.. A sparky once put it on the right setting for testing resistance for me and that's where its stayed.. To be honest the numbers mean nothing to me. I just check the mat before laying it, after laying and and before I leave the job after tiling..
 
That’s ok for the functional side of the mat but for safety reasons the integrity of the wiring to earth needs to be checked too..
worst case scenario would be naked homeowner doing the moonwalk and tap dance across the bathroom floor :tearsofjoy:
 
Unfortunately that meter can’t do the necessary test..
Strima posted a link to what you need..
May should be tested before and after installation..
I would also test it once you have laid it and prior to fixing tiles down
 

Reply to UFH question for a tiler.. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock