they look like white old color cables so its gonna be a while they in there. any signs of thermal damage? if not then stick some cable ties on the bunch to keep it away from the nearest pipe and leave alone.
you're unlikely to lift the floor boards for an EICR.
and whats that bit about cables need to be more than 50mm below floor ?

Have to agree, not much you can do other than noting it on the cert (assuming you are doing an EICR?). Unless of course the customer wants to pay for rectification work to correct it all![]()
Hmmm......if you are considering thermal degradation, then the last thing you'd want to add into the equation (no pun) is bunching!

BGB reg 522.6.100 A cable under the floor should be at least 50mm measured vertically from the top or bottom of joist.... or be mechanically protected and so on , As far as I can see even if the cable is RCD proected this reg applies
And yes I agree you are unlikely to lift floor boards durring an EICR it was a leading question![]()

and have you had the client`s permission to carry out this work?The concrete joist has plenty left in it to take more of a bash, is 9"x 9" thick; and am looking to covering the cables with two trunking trays clipped together to create a box, and additional plating across the top as this board is in a doorway.
Possibly lagg the pipes as well (though minimal space).
The cables have no sign of thermal damage... just blackening for mice squeezing through in the past, and yes checked by wiping clean to be sure![]()
and have you had the client`s permission to carry out this work?

The concrete joist has plenty left in it to take more of a bash, is 9"x 9" thick; and am looking to covering the cables with two trunking trays clipped together to create a box, and additional plating across the top as this board is in a doorway.
Possibly lagg the pipes as well (though minimal space).
The cables have no sign of thermal damage... just blackening for mice squeezing through in the past, and yes checked by wiping clean to be sure![]()
Sounds like a plan just make sure you keep the metal plate away from the pipes or you will just transmit the heat from the pipes to the plate , No need to earth it though