they look like white old color cables so its gonna be a while they in there. any signs of thermal damage? if not then stick some cable ties on the bunch to keep it away from the nearest pipe and leave alone.
 
they look like white old color cables so its gonna be a while they in there. any signs of thermal damage? if not then stick some cable ties on the bunch to keep it away from the nearest pipe and leave alone.

Hmmm......if you are considering thermal degradation, then the last thing you'd want to add into the equation (no pun) is bunching!
 
you're unlikely to lift the floor boards for an EICR.
and whats that bit about cables need to be more than 50mm below floor ?

BGB reg 522.6.100 A cable under the floor should be at least 50mm measured vertically from the top or bottom of joist.... or be mechanically protected and so on , As far as I can see even if the cable is RCD proected this reg applies

And yes I agree you are unlikely to lift floor boards durring an EICR it was a leading question :)
 
Have to agree, not much you can do other than noting it on the cert (assuming you are doing an EICR?). Unless of course the customer wants to pay for rectification work to correct it all :-)

No was just doing an addition and amendment to circuits when I uncovered this one.
 
Hmmm......if you are considering thermal degradation, then the last thing you'd want to add into the equation (no pun) is bunching!

Thought that strait away myself, once the heating was all up and running was thinking of doing a loop test at the furthest points with heating on. (just for research). As it is a friends house and will be getting a EICR/periodic inspection completed by a full sparky, As a domestic installer, can only do installs, amendments, and additions..... for now :)
 
BGB reg 522.6.100 A cable under the floor should be at least 50mm measured vertically from the top or bottom of joist.... or be mechanically protected and so on , As far as I can see even if the cable is RCD proected this reg applies

And yes I agree you are unlikely to lift floor boards durring an EICR it was a leading question :)

As it is placed in a door way I was thinking of installing some sheeting over (earthed if metallic).
 
The concrete joist has plenty left in it to take more of a bash, is 9"x 9" thick; and am looking to covering the cables with two trunking trays clipped together to create a box, and additional plating across the top as this board is in a doorway.
Possibly lagg the pipes as well (though minimal space).
The cables have no sign of thermal damage... just blackening for mice squeezing through in the past, and yes checked by wiping clean to be sure :)
 
The concrete joist has plenty left in it to take more of a bash, is 9"x 9" thick; and am looking to covering the cables with two trunking trays clipped together to create a box, and additional plating across the top as this board is in a doorway.
Possibly lagg the pipes as well (though minimal space).
The cables have no sign of thermal damage... just blackening for mice squeezing through in the past, and yes checked by wiping clean to be sure :)
and have you had the client`s permission to carry out this work?
 
and have you had the client`s permission to carry out this work?

Yes they are friends, and want me to make the system as safe (and up to current regulation) as possible for rental.
I would not take any more out depth wise, just widen by about 2 cm.
 
sounds a good plan. but no need to earth the metal protection plate/s .
 
Hey, here's one I found. Was hiding under the floor, nestling snugly against a central heating pipe. Was like peeling sunburn :rolleyes2:, but it was the borrowed neutral that nearly got me :icon9:..... I must test neutral to earth before touching, I must test neutral to earth before touching, write out 100 times and dont do it again!!
IMG_0136.jpg
 
The concrete joist has plenty left in it to take more of a bash, is 9"x 9" thick; and am looking to covering the cables with two trunking trays clipped together to create a box, and additional plating across the top as this board is in a doorway.
Possibly lagg the pipes as well (though minimal space).
The cables have no sign of thermal damage... just blackening for mice squeezing through in the past, and yes checked by wiping clean to be sure :)

Sounds like a plan just make sure you keep the metal plate away from the pipes or you will just transmit the heat from the pipes to the plate , No need to earth it though
 
Sounds like a plan just make sure you keep the metal plate away from the pipes or you will just transmit the heat from the pipes to the plate , No need to earth it though

Yup was a concern, but now thinking of fitting small strip metal plates on the floor to stop screws as I will also be helping with the flooring.

Zebra Strips - close call by the sounds of it, can I post your pic on FB to illistrate what I have been trying to explain to clients, have not come across a cable like this from heating pipes.
 