Hi,

Doing CU change & no wires larger than 2.5mm, however, appearing from under floorboards are 2 x 6mm cables, 1 is live, in the approved fashion, the other live on live, neutral and earth (Yes, I know), before being connected to a 2.5mm & off to a socket.

I am unable to tear apart the house to investigate fully, & If I disconnect the circuit & make the problem wires dead, I also disable some sockets that are fine and needed.

Have spent too long on this problem and am in need of wisdom and whisky.

Helpful suggestions welcome. (On the electrical stuff, I know enough about whisky)

Thanks
Jim
 
Not entirely sure I'm understanding you - are you meaning to say that in one 6mm T&E the live is live, and in the other 6mm T&E you have 230V referenced to earth on both the L and N conductors?

Either way, I'd suggest that the 6mm has simply been used as it happened to be there already (very common to find 6mm feeding sockets in kitchens after a cooker cct has been moved, for example) and that somewhere there's a JB from some 2.5 > 6mm.

But please clarify the problem and I'm sure we can help. What tests have you done so far?
 
That needs investigating fully. There is nothing else that would be acceptable in my opinion. I definitely would not be reconnecting it.
 
Don't think there is much as you can do, but investigate further, charging the customer though. The existing installation sounds a bit DIY'y. Isolate, leave and go back with a fresh perspective.
 
The earth , neutral and live are all live, & the JB is nowhere to be found.

If you're measuring the N & E, what are you using as your reference? As in, L-N = 230 (fine), N-?, E-?
 
This cable needs to be isolated asap, if your saying live across all 3 poles, can you measure the voltage?if so what are you reading?.
 
If you have bare live wires, which are connected to a circuit yo ucan't leave switched off you can only do one thing. Get a 60A JB, terminate the live cable into the JB and secure where it will be accessible in the future.

PLUS obviously a note on the cert.
 
It is a radial, but , obviously, the 2 ends of 6 mm cable are not the same cable (or they have a JB between them, which I cannot see)

Not on site at the moment, have switched off & back monday with fresh ideas

thanks for your suggestions
Jim
 
So you HAVE left it switched off and you stated in the OP that the sockets are required.

Whats the rating of the OCPD?
 
If you have bare live wires, which are connected to a circuit yo ucan't leave switched off you can only do one thing. Get a 60A JB, terminate the live cable into the JB and secure where it will be accessible in the future.

PLUS obviously a note on the cert.

Apart from the fact that in this case the bare wire is apparently the CPC, and if we're talking 6242Y will have no insulation nor ident. As you rightly say, until we can get some more info out of the OP it needs isolating in a substantial way.
 