Surely the first principle is to ensure earthing and bonding is all correct and the earth rod/mat etc gives the lowest Ra possible so any touch voltages are as low as can be? Or am I missing something?

As an aside the only RCDs I've ever known to fail testing were MK and Wylex ones, so maybe ensure you have good quality equipment?

Mine is wylex, go figure.

This is where my knowledge is hazy so correct me if I'm wrong. Is it possible get touch voltage down to acceptable levels on a TT system?
 
So the rcd itself plays a major role in allowing this to be satisfied?
Yes , without an rcd it's virtually impossible to achieve your disconnection times with a live to earth fault.
E.g. Ra of 150 ohms x 0,03 = 4.5 volts.
Ra of 150 ohms x just 0.4 of an amp =60 volts
50/0.03 = 1667 ohms max resistance before 50v touch voltage exceeded
 
An RCD will have no effect on the touch voltage. All it will do is ensure that the fault is disconnected in the required time.
 
Dirk, there's a simple answer here mate. Fit a 100mA time delayed RCD up front.

This is the problem with domestic TT systems. More often than not they rely on 30mA RCDs for both additional and fault protection, so if one fails, which they regularly do, and a fault occurs, this is a dangerous situation.

The time delayed RCD isn't there to provide additional or fault protection but is there merely as a back up if one of your 30mA RCDs fails and a fault occurs.

The discrimination comes in the form of the time delay. If a fault occurs and your 30mA RCDs are functioning as intended, you'll want the relevant one of these to trip knocking out at most half your board. You don't want an up front RCD tripping unecessarily and knocking out your whole board.

There is no requirement to fit back up protection to a TT system, but it's very good practice. No domestic TT system I ever install is complete without it.
 
Thanks D. It wouldn't matter to me if the up front RCD tripped as my board isnt a split load, if my RCD trips now it takes the whole board anyway.

One of the sparkys I spoke to said two 30ma RCD`s affect each other and cause nuisance tripping, ive never heard of this before though, has anyone else come across this?
 
Thanks D. It wouldn't matter to me if the up front RCD tripped as my board isnt a split load, if my RCD trips now it takes the whole board anyway.

What would matter though is easy identification of a fault. With a time delay up front, if that trips you almost certainly know the 30mA one is buggered.

One of the sparkys I spoke to said two 30ma RCD`s affect each other and cause nuisance tripping, ive never heard of this before though, has anyone else come across this?

On test they can do yes. Two RCDs in line won't affect each other under normal operating conditions, you just never know which one will go first, if not both at the same time.

If you haven't got a split load board, you're not creating a problem by adding a 30mA up front, but I'd still recommend a time delay. Cost wise there's not a lot in it.
 

Reply to Up front Rcd question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
921
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock