Just wanted a bit of advice about Earthing!! I'm not too sure whos responsibility the Earthing conductor is from the earth block to the cable sheath? It's 4mm and before I give out any certificate for a CU change I want to see 16mm. All other bonding and earthing needs upgrading as well but it was just this bit I was unsure about as I thought maybe its the DNO's field?


earthing size.jpg

Cheers..
 
DNO earth. leave as is. just work from MET . if Ze is >0.8, contact DNO.
 
Thanks Telectrix.

Ze is 0.15. I will upgrade all my earthing and bonding bits to current regs but leave that bit. Am I still able to give a cert?
 
Just seems a bit odd.. I'll put down 16mm for earthing on the cert when I've upgraded my bit knowing that theres a 4mm link to the sheath from the earth bar.

Quite agree with you but if the 4mm is fixed to the DNO head you can't change that and from your OP the Ze is fine so I'd be finishing off the cert and raising an invoice!
 
for an old TNC-S connection to the sheath, that id the dog's danglies. usually it's only about 2.5mm bare.
 
If that's an earth wire connected to a ring type clamp with a nut and bolt onto the lead sheath,I would and have changed these countless times,if not ignore me I have a mammoth job to see pictures anyway lol
 
If that's an earth wire connected to a ring type clamp with a nut and bolt onto the lead sheath,I would and have changed these countless times,if not ignore me I have a mammoth job to see pictures anyway lol

No nut and bolt, firmly soldered into place :smiley2:
 

Reply to upgrading main earthing? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
280
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
739
Hi All I have been asked to supply a minor works certificate on a smart thermostat upgrade. Would I just test the dedicated circuit from the CU...
Replies
3
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock