Hi all. I have a couple of outbuildings which I laid cables to from the house. Both are about 130m cable runs away individually.

Just thinking about the time it takes for a RCD to "trip" - do I need to put RCD's in the distribution units? at the buildings? Also I presume it would be wise to also fit a good earth rod too.

Any advice would be greatly received.
 
So I see most of the "garage" consumer units have RCD's in so I guess multiple RCD's on a circuit is OK. Our earthing in the house is TN-C-S - but we are out in the sticks and with overhead wires - which we have lost once before in a gale since we have been here - so an earth rod I guess would be prudent.
 
i'm confused. why do you mention multiple RCDs? each outbuilding should have it's own RCD, independent of the other. what cables have you installed (type, no. of cores, size).
 
10mm 3 core SWA. Just required for lights and a plug socket.
 
Last edited by a moderator:
one cable or two? estimated load for each outbuilding. c'mon mate more info. this is like pulling teeth.
 
SWA is a cable used as an alternative to RCD protection and for situations where RCD protection is not acceptable.
 
There is an excellent guide to power for outbuildings here
http://electrical.------.org/wiring-matters/16/elect-inst-outdoors.cfm?type=pdf
This was written under the regulations of the 16th, but still valid.

Normally you do not have an RCD at the supply end but you do at the remote end. You don't want a 260metre trek back to the house every time the RCD trips!

So, RCD at remote end, none at the source end and yes a separate earth rod for each outbuilding with the usual precautions if you have livestock out there!
 
You don't want a 260metre trek back to the house every time the RCD trips!

I've been seeing this type of comment a lot. Just out of interest, how many times has your RCD tripped in the past two years?

Someone should set up a pole to see how often RCD's trip for the people on this forum..
 
Thanks everyone. Info - sorry - two separate cable runs on different directions - total 130m each not 260m total. Load is for a few lights and a plug. Cant see any more than about 10A required peak max - mainly lights at say 300w.

One last question - no RCD at the source end - what is the proper way to bypass the RCD in my house distribution board then - job for my sparkly this one :) - and to run his eye over what I have done.

And one more last question... Can I terminate the SWA cable in a Wiska box next the distribution board and then cable from that. You can't really fit glands to a domestic distribution board. Also the earth. Earth rod to distribution board - then can I piggy back from that to earth the SWA armour or should it have it's own? - sorry if that is in the guide - I have not read that as yet.
 
If you are not an electrician but are getting an electrician to oversee this installation, then all questions regarding the installation would be best directed at them.
 
If you are not an electrician but are getting an electrician to oversee this installation, then all questions regarding the installation would be best directed at them.
I absolutely agree. You need an electrician on site to advise and design. There are so many gotchas, especially these days with AMD3 requirements and TT supplies being near the top of the list. In any case, this is NOTIFIABLE work!

Re the 260metre comment. That was my take on how far you have to walk if you in the outbuilding and trip the house RCD. Its then 130 metres to the house and another 130 back again..

As an overview here what i would do.

House end. Henley block supply and provide a mini DB with 100mA Time Delay RCD. two MCBs one for each cable to the outbuildings. Armour earthed from this end ONLY. This gives protection for the cables.

At the outbuildings a mini DB with 30mA rcd. Separate earth spikes making the supply types
in the outbuildings TT. MCBs for the lights&sockets in each outbuilding.
 
I've been seeing this type of comment a lot. Just out of interest, how many times has your RCD tripped in the past two years?
Not many. But then I like to think I have an appreciation of things, electricity-wise.

I'm looking at the worse case, we don't know what he's going to plug in. A dodgy power tile cutter, a crappy outside light, failing pond pump, faulty milking machine, who knows...
 
I absolutely agree. You need an electrician on site to advise and design. There are so many gotchas, especially these days with AMD3 requirements and TT supplies being near the top of the list. In any case, this is NOTIFIABLE work!

Re the 260metre comment. That was my take on how far you have to walk if you in the outbuilding and trip the house RCD. Its then 130 metres to the house and another 130 back again..

As an overview here what i would do.

House end. Henley block supply and provide a mini DB with 100mA Time Delay RCD. two MCBs one for each cable to the outbuildings. Armour earthed from this end ONLY. This gives protection for the cables.

At the outbuildings a mini DB with 30mA rcd. Separate earth spikes making the supply types
in the outbuildings TT. MCBs for the lights&sockets in each outbuilding.


I have to agree with this install but question what are your thoughts behind the 100mA rcd at house side what are you achieving with this that a main switch doesnt?
 
I have to agree with this install but question what are your thoughts behind the 100mA rcd at house side what are you achieving with this that a main switch doesnt?
The cable to the outbuilding would be protected by an MCB, lets say its 32A. If there is an earth fault on the cable the MCB should trip, but the earth fault current will be restricted by the impedance of the earth/ROD at the house and, and that is never going to be enough to trip a 40A MCB.
So an RCD is needed to provide this protection. Its not for personal protection, so 100mA fits the bill, but it needs to be time-delayed or an earth fault in the outbuilding could trip both the remote 30mA RCD, and the 100mA RCD at the source end.
 
No rod at the house, house is TN-C-S.
Although it should be mentioned that there is nothing inherently wrong with having an earth electrode installed with a TN-C-S supply. (In fact much of the world requires this!)
 

Reply to Use RCD for 130m cable run to outbuilding? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
883
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
789
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
721
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock