YTSOxford

Right.
I have added a couple of garden lights onto a radial circuit that is in a garden for a pond etc. However as always the contractor supplies the cable. New board in house, the cable to the pond 2.5mm 3 core swa...up to 17th etc... but i have only been given 2 core swa 1.5mm.

So I am using the armour as the earth in this case, as I remember from 17th update, the tutor saying this is fine. But what I can't get my head around is.... The lights are metal, so terminating at each end, does this not produce eddy currents???

Discuss:)
 
Right.
I have added a couple of garden lights onto a radial circuit that is in a garden for a pond etc. However as always the contractor supplies the cable. New board in house, the cable to the pond 2.5mm 3 core swa...up to 17th etc... but i have only been given 2 core swa 1.5mm.

So I am using the armour as the earth in this case, as I remember from 17th update, the tutor saying this is fine. But what I can't get my head around is.... The lights are metal, so terminating at each end, does this not produce eddy currents???

Discuss:)
I thought that eddy currents occurr with single core cables?
 
concur with eddies in singles, if memory serves they occur i twins but cancel themselves out, i use the armour as cpc every time, but dont no what to put on cert.for cpc cross section,just put the min required ,1.5 for 2.5 cores etc.
 
concur with eddies in singles, if memory serves they occur i twins but cancel themselves out, i use the armour as cpc every time, but dont no what to put on cert.for cpc cross section,just put the min required ,1.5 for 2.5 cores etc.

I put S or SWA,and put a reference to it in legend.don't know what you are SUPPOSED to do.
 

Reply to Using armour as cpc in the Australia area at ElectriciansForums.net

Similar Threads

Hi, someone has ordered Steel Tape Armoured cable instead of SWA. Can I use this armour as a CPC the same as SWA or not and if so is there a table...
Replies
13
Views
1K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
4K
https://gadsolutions.biz/regulations/swa-as-the-cpc Anyone know how reliable the tables on this website are for determining whether the armouring...
Replies
13
Views
3K
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock