ringer

Why is it most timers state that they are not suitable for use with discharge lighting? I understand that discharge lighting (e.g. SON lamps) are an inductive load, but what will happen to the timer is used to control such a load? Will the timer just cease to function? Or is it a potentially dangerous combination?

examples of timers looked at

Grasslin 24hr socket box timer
Timeguard FST11A
 
it will cause excessive arcing across the contacts. use the timer to contol a relay, or contactors
 
Have found what usually happens in the contact sticks on so will not turn off, the best option is a sangamo timer but the cost puts most off, the cheaper option is a standard timer and heating contactor in an enclosure.
 
The switching off of an inductive load causes a large back emf which arc across the opening contacts if not rated, this damages the contact points and can lead to loose contact giving rise to excessive heat which in-turn weld the contact shut, to get around this use an appropriate rated contactor and have the timer pull the contactor in which in turn powers the inductive load. This tends to be cheaper than using a rated timer.
 
have come across this problem many times,as i do a lot of work for blocks of flats and have found the best solution is to stick with the expensive Sangamo timers(get what you pay for) or basic Immersion timer like you mentioned in conjunction with a lighting contactor in a small enclosure next to it.Is it not possible to use photocell instead even if used with a timer as the contacts on the photocell are usually better than the timers(depending on load of obviously)
 