evening all!

problem with speed controller operated commercial ecxtractor?

mcb tripped then push reset on controller. ok for a few minutes, although not running at full power, then fast blow fuse in controller blown?

would the fan work directly from mains, through mcb, to test
fan itself?

or any suggestions pleade?
 
Did you IR test the fan and check the windings. Also test the capacitor if there is one. You can connect the fan directly onto the supply to test it but the MCB is sized to the cable, not the load on the end of it so the fan will not be protected against overload. Things will go downhill rapidly if there's even a minor problem and by the time the MCB trips the fan will already be history.
 
thanks for the replies,

i'm going back today to sort it out, the fan is caked in grease so i've asked them to give it a clean up if poss!

i'll post again when i know more.

as it was 9.30 on a sunday night, i didn't do much more than a bit of finding out, then ordered some supper from them!
 
an update. the fan's knackered!

managed to get supply through controller up to fan terminals, changed capacitor, as it was a cheap maybe, but still no joy.

£400 plus vat for new fan, ordering tomorrow, delivery day after direct from vent axia, then a lovely changeover, ans apparently some minor alterations to ducting fixings!
 
does it have to be connected via a fan speed controller?

from some of the replies, i take it there is some protection for the fan built in to the controller?
 
No it doesn't you just have to move the speed pack (capacitor block) from the controller to the fan and plug it in according to the speed you require
 

Reply to vent axia problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
985
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi, I have a project I have been working on, that has me out of my depth with regard to my knowledge, as I am a very basic electronic hobbies...
Replies
5
Views
935
Has anyone taken apart their & self repaired it? 2013 Dodge Grand Caravan SXT - Mileage: 112223 - DTCs - P0480 cooling fan. Also codes in TIPM...
Replies
0
Views
639
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock