wouldn't like to see the state of a 1.5mm cpc after 24KA been up it , even for a fraction of a second.
I had a Fluke 1652 giving me readings like that once, sent it off to be calibrated all came back ok, but it still gave random readings, its now in the stores! Test at a socket then at the mcb for that circuit (not at main switch as the RCD needs to be taken into account). then at the main switch. Tell us what readings you get
I don't think some of my posts are being sent. I have tried my three probes at my socket terminals and am getting 0.01ohms with a PEFC of 24Ka. So I think the problem is solved.
Just one more thing; I had a RCD main swith ch trip on me whilst carrying out Zs test the other day. I need to go back and sort it ( It's an empty house) What could be causing the RCD main switch to trip? I was using my plug adapter again>
Many thanks.
I would say that the problem here is far from solved. Firstly, I don't believe that figure for a second, so something wrong with either testing or meter. Secondly, do you know what a standard switch/MCB is rated at? Certainly not 24KA!!!
24KA - jesus - I never really see more than 2KA around my next of the woods.
Seen 5.9KA in London which if I recall is the highest I have seen.
Are you local to Essex? if so you can borrow my spare calibrated meter if you like.
Reply to Very high Zs reading in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...