T

trevthelec

hi, I have ariston boiler with volt free connection ,ta1, this should have been plumbed with 2x 2 port valves as recommended by manufacturer , but plumber has installed 3 port valve so we have to put relays in can anyone put me in right direction with wiring from wiring centre to relays?
 
Connect the orange of the valve and normally closed of the cylinder thermostat to one side of the coil, neutral to the other side of the coil, one side of the TA1 connection to common of the relay and the other side of TA1 Connection to normally open of the relay.

If you get an 8 pin relay base connect orange and normally closed of cylinder thermostat to pin 2, neutral to pin 7, one side of TA1 to pin 1 and the other side of TA1 to pin 3.

2 Pole 8 Pin 230VAC Relay Round Terminal - https://www.electrical2go.co.uk/2-pole-8-pin-230vac-relay-round-terminal.html

Round 8 Pin Relay Base - https://www.electrical2go.co.uk/round-8-pin-relay-base.html

Multi Purpose Enclosure - IP66 with 35mm DIN Rail - Solid Lid | QVS Direct - https://www.qvsdirect.com/multi-purpose-enclosure-ip66-with-35mm-din-rail-solid-lid-14665
 
Can’t you use the auxiliary switches on each valve,these then connect to boiler connections.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
volt free wiring on y plan
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
trevthelec,
Last reply from
trevthelec,
Replies
8
Views
3,288

Advert