Discuss Voltage drop under load in the Need help with ElectriciansForums.net? area at ElectriciansForums.net
Hi, has anyone encountered a similar fault...
TN-C-S supply with old wylex fusebox. Last night, customer experienced total power loss whilst in the shower (electric), nothing tripped and no fuses blown. Customer pulled out fuses to check them and then replaced them all but could only get some lights & TV to work.
I tested voltage on supply side of main switch (220v) in the 'OFF' position and (210v) in the 'ON' position, but then as soon as anything is plugged in, or a light is turned on, voltage instantly becomes unstable, bouncing around between 115v - 180v. Disconnecting the shower made no difference.
I did an insulation resistance test across all circuits and readings are around 48-50MΏ on L-N, L-E & N-E.
I've not seen this kind of fault before. Has anyone else? any suggestions for further investigation would be really appreciated.
Sounds like a bad connection on the supply side, if the service head is getting hot under load it could be in there. If it's an overhead supply, it could be a bad connection along that route.
Reply to Voltage drop under load in the Need help with ElectriciansForums.net? area at ElectriciansForums.net
Just had a call from an M&E client of mine and good mate asking to pick my brains.... large 3ph biomass boiler with (I assume variable speed)...
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
  • Locked
5K
Hiya lads I was asked to have a look at wiring in a recently installed kitchen as some of the appliances tripping the rcd when on. The kitchen was...
Toneyz
T