voltage drop

  1. AngelLaHash

    Random Voltage Drop from 236v to 120v

    BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has continuity even trust the RCCB that it trips. All ok but i noticed on phase for a short while it dropped to 120v on my meter.. just Random comes and...
  2. H

    Voltage drop help please

    all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm potentially doing something wrong. Here comes de Q. Voltage drop of a single-phase distribution circuit supplying a power distribution board in a remote...
  3. D

    Measuring Voltage Drop - With or without Load?

    I am sending power to some 5v led lights about 50ft from the transformer. I was going to use some CAT6 direct Burial cable that I kept after a contractor accidently cut it (I replaced the wire as I did not want to do an underground splice). So I plan to use 1.5 pairs (three conductors) for Pos...
  4. B

    3 phase voltage drop calculation?

    Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm 90 degree SWA, 45 meter run. 30,000/sqrt3/400 = 43.3A = Ib from the table 4E4B, a 10mm cable gives 4.7 So then 43.3 x 4.7 x the 45 meter run gives =...
  5. B

    Single and three phase current capacity and voltage drop differences.

    Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three phase, do I take the max power, divide by 3 then divide by 230 to get the Ib? (We definitely use 230V for everything right?) Now for voltage drop, We...
  6. W

    240v outlet voltage drop under load

    I have a 3 prong 240v outlet for a dryer that reads 240v across both legs and 120 across the ground. When I turn the dryer on and have the multi meter to the ground and a hot leg it shows 120 but if I switch it to the b leg and ground it shows 40 then climbs up slowly to 120. The ground is new...
  7. S

    Trying to figure out alternatives for remote accessory structure

    Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and building a new house but am not an electrician. I'm researching options for getting power to a small cabin in the woods behind a house (Oregon, USA). It...
  8. J

    Voltage drop question

    I have a run of conduit 172ft from a 12x12 box which branches out to parking equipment with runs about 50ft from the box. My voltage drop calc requires me to run #10s to the 12x12 box. My question is from that box can I size down to the respected size of wire my machines need (#14awg) to branch...
  9. M

    Voltage drop sin phi

    Hi chaps, Been working though the electrical design guide and I'm stumped on reactive power. volt drop and the equations are easy enough but I have no idea where sin phi has come from or how they have calculated it at 0.6. Any help would be greatly appreciated
  10. I

    Rio and BHP specs for unsupported cable allowance and Voltage drop?

    Hi senior members of the forum, I need advice on couple of questions about Rio and BHP specs for electrical installation purposes. What is the minimum allowance for unsupported cable coming out of cable ladder. This is for install of a genset trailer to load. The cable will be going through...
  11. P

    voltage drop running 50 amps 350 feet from service pole.

    hello. i need to run power to a cabin that is 350 feet from the service pole in our driveway. the problem is voltage drop. the service pole is 150 feet from the transformer so total run is 500 feet. is it possible for a diy'er to purchase a small transformer that would bring the voltage up? (i...
  12. E

    Voltage drop when transformer on site

    I've got what may be a stupid question but the only answer that I can come up with is 'because it says so in AS 3000', is there a reason why you only get 5% voltage drop when your transformer is on the site but not dedicated to the site? To me, the physics would suggest that it should be no...
  13. Y

    12V voltage drop dual battery camper installation

    Hi there I can't wrap my head around a problem I have when trying to connect my dual 12v battery system in a camper. When I plugged in my VSR ( Orion from the brand Victron) i measured the + input was 3 volts although engine running (and app saying 14v input...). I thought the wire were too...
  14. Daniel DD

    Surge Arrester Installation and External Short Circuit Protection Device

    BACKGROUND I live in a small town where it is difficult to find ceritified electricians. In fact, electrician certification is not common for residential installations. I did find some experienced electricians but I don't think they are certified and know best practices in the installation. I...
  15. M

    Circuit length and voltage drop

    Hi, I'm currently doing my assignment for 2357 and was just making sure I'm calculating the cable length for the lighting circuits right. As depending which way you do it, it alters the voltage drop a bit. On the drawings I've looped in and out at the switches all the way to the final light...
  16. K

    24volt voltage drop on a multiple garden LED layout design? Best practice?

    Hi all, This is my first time posting something on this forum. I'm busy putting together a design for some LED lights that are going to be mounted on some columns along a pathway. The supply will run twenty odd metres to an enclosure on the outside of the building that will encase the...
  17. G

    complex voltage drop question

    The project: Install 12VDC 3 Watt Low voltage LED pathway lights, one every 20', along a 420' boardwalk through a mangrove forest. There are 24 lights and to minimize taps in the main line they will be installed in groups of 3 with one light at the tap, one light 20 feet behind and one 20 feet...
  18. E

    DC Wiring help

    Im looking for some advice on some dc wiring i have in place. Currently i have some monitoring equipment that wont run when connected to a run of wire about 40m long (1.5mm diameter) it is connected to a 12v 100ah battery and what i think is happening is the voltage drop over that distance is...
  19. P

    Excessive voltage drop, HELP

    So, I have encountered strange problem. Thing is when I connect load with power about 30w my voltage goes from 227v to 170v it is single phase system. Wires are brand new and thick enough. Is it maybe a problem in power company transformer voltage stabilizer or something else. Im also curious if...
  20. P

    Voltage Drop at an RV Park

    First, I really appreciate any feedback you can provide. Its awesome to have a group of people that have a passion for this! Our RV Park has a transformer dropping service down into three 200-amp meters (single-phase 240V service X 3). From each of these three meters, we have an emergency...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock