all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm potentially doing something wrong. Here comes de Q.


Voltage drop of a single-phase distribution circuit supplying a power distribution board in a remote building is to be verified as part of the periodic inspection and testing within a workshop complex. The installation forms part of a public 400/230 V TN-S system. The circuit has a measured R1+Rn value of 0.15 Ω and an Ib of 60 A. The circuit protective device has an In of 80 A. What is the voltage drop for this distribution circuit?
mv/A/m × ib × l
1000
According to the mock test the right answer is 10.8V however with result was a little bit higher .

2.8x60x65/1000= 10.92v

Table 4D1B osg
16mm
Mvam 2.8
Could anyone point out where and what I'm doing wrong . TIA
 
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm potentially doing something wrong. Here comes de Q.


Voltage drop of a single-phase distribution circuit supplying a power distribution board in a remote building is to be verified as part of the periodic inspection and testing within a workshop complex. The installation forms part of a public 400/230 V TN-S system. The circuit has a measured R1+Rn value of 0.15 Ω and an Ib of 60 A. The circuit protective device has an In of 80 A. What is the voltage drop for this distribution circuit?
mv/A/m × ib × l
1000
According to the mock test the right answer is 10.8V however with result was a little bit higher .

2.8x60x65/1000= 10.92v

Table 4D1B osg
16mm
Mvam 2.8
Could anyone point out where and what I'm doing wrong . TIA

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm potentially doing something wrong. Here comes de Q.


Voltage drop of a single-phase distribution circuit supplying a power distribution board in a remote building is to be verified as part of the periodic inspection and testing within a workshop complex. The installation forms part of a public 400/230 V TN-S system. The circuit has a measured R1+Rn value of 0.15 Ω and an Ib of 60 A. The circuit protective device has an In of 80 A. What is the voltage drop for this distribution circuit?
mv/A/m × ib × l
1000
According to the mock test the right answer is 10.8V however with result was a little bit higher .

2.8x60x65/1000= 10.92v

Table 4D1B osg
16mm
Mvam 2.8
Could anyone point out where and what I'm doing wrong . TIA
Hi helio007 , I think they have used a different calculation but your answer would also be right.
They seem to have used the 0.15 value,

0.15 x 60 x 1.2 (70 degrees ) = 10.8v,
 
According to the mock test the right answer is 10.8V however with result was a little bit higher .
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute the drop cold as 60 * 0.15 = 9V

You are then assuming this will run hot at the usual CCC rating of 70C so you have a further 20% rise in R1+Rn so you get 9V * 1.2 = 10.8V
2.8x60x65/1000= 10.92v

Table 4D1B osg
16mm
Mvam 2.8
Could anyone point out where and what I'm doing wrong . TIA
If you are planning the circuit then you would use this, but the fact is you have a measured value, which allows for cable length and tolerance more precisely, so you should use that instead. Of course you should see if it is close the the expected value in case of some error (wrong calculation, length longer/shorter than planned, poor junction if cable not continuous, etc) but as this is only about 1.1% difference you can safely assume it is OK.

Remember also that the value of 2.8 mV/A/m looks rounded to 1 digit, so it could be 2.8 +/- 0.05 which is +/- 1.8% on the tabulated value, greater than the difference in answers. Of course, your meter is probably only 3% + couple of digits, so unlikely to be much better!
 

Reply to Voltage drop help please in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
770
Hi all, I am currently doing my 2391-52 and have been given a mock paper, one of the questions is around vold drop as per below, can someone...
Replies
20
Views
5K
Select (Scottish) Certification Scheme Question on volt drop from 2391
Hi all, I have worked out the volt drop on other questions using the formula mVxAxM. had no issues, but this question below has just fried whats...
Replies
26
Views
6K
Morning team Question about volt drop. I presume I am missing something here. So firstly the facts out the OSG. Table 7.1, page 66, lighting...
Replies
20
Views
3K
S
Determine the minimum size of cpc for the circuit giving consideration to; Disconnection times Thermal Constraints? Here is what I have worked...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock