Discuss Volt drop maths in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

The formula is in BS7671:2008 for working out the correction factor, I seem to remember involves square routes, as far as the 26 amp for ring final never found it written down, I was attending IET lectures when BS7671:2008 came in and in the lecture it was stated moving from the 4% for all to 3% lighting and 5% power resulted in the length of a ring final going from 80 something meters to 106 meters, however try as I could I could not get this 106 meters, so I asked and was told we consider 20 amp draw at centre and 12 amp even spaced so use 26 amp as design current. I have never found this written down, but it does give the 106 meters of 2.5 mm cable being just within volt drop limit.

With lights of course there is nothing to say 6 amp is the design current, it could well be considered as 3 amp if all lamps even spread, so 3 amp at 3% volt drop would allow 91 meters of 1.5 mm cable. If the DNO loop impedance is 0.35 ohms the end of run loop impedance should be 3.25 ohms.

However in real terms since only line goes to switch, not that easy to work out the limit.

My worry was if I do an EICR and say all is OK and there is excessive volt drop, could some one at a latter date say I got it wrong and try to claim I had not done the EICR correctly, or PIR as it was called then, however one there are laid out forms to show an EICR results and also set criteria as to issuing C1, C2, C3 etc. And unless volt drop was massively over limits it is unlikely to be picked up on.

My original idea was to include the calculations in the test results to auto flag up if non compliant, but a loop impedance meter is not that accurate, test three times and you will normally find 0.02 ohm variation, this is doubled up when also measuring the DNO at head loop impedance, 0.04 ohms makes a big difference to volt drop calculations, and if for example it was found you had 130 meters instead of 106 meters, all you need to say is worked at at 13 amp at centre and 19 even spread so using 22.5 amp as design current, and no one can say that's wrong.
 

Reply to Volt drop maths in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
863
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock