When calculating voltage drop and using the formula

mV/A/m x Design Current x length / 1000 = v

Do I use the design current value after rating factors have been applied?

Thanks again for any help.
 
When calculating voltage drop and using the formula

mV/A/m x Design Current x length / 1000 = v

Do I use the design current value after rating factors have been applied?

Thanks again for any help.

No you would use your design current, Ib.
Design current after derating factors is no longer design current.

Think about the calc. Design current is what you want the circuit to be able to continuously handle.

Derated values only apply to the cable used for that job.
 
Check your units! Basic computation is:

voltage = (design current) x (resistance per unit length) x (length)

For whatever reason the resistance[*] is often given as volt/amp/km or similar. The volts/amp part is ohms and if it is given per km then it is equivalent to milli-ohm per meter (1ohm/1000m => 0.001 ohm/m).

As already explained the current after the various derating factors is used to select a cable from a current carrying point of view due to heat and is not a 'real' value from a circuit point of view. Rather than try to adjust cable specifications according to the environment, it is simpler to compute an "equivalent heating current" that you can then use with tables of cable capacity under basic conditions.

* Strictly speaking it is impedance but for most cables it is mostly resistance so we will call it that!
 

Reply to Voltage Drop Design Current? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
699
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
575
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
1K
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
I am sending power to some 5v led lights about 50ft from the transformer. I was going to use some CAT6 direct Burial cable that I kept after a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock