Murdoch agreed but a screwed down board in a non carpeted room is as accessible as a bit of ply over main incoming supply which I see quite a lot but I suppose that's inaccessible too

Yes BUT, the next day they could lay lino or tiles.... so under floorboards is INACCESSIBLE, unless there is a cellar without a ceiling.
 
Murdoch agreed but a screwed down board in a non carpeted room is as accessible as a bit of ply over main incoming supply which I see quite a lot but I suppose that's inaccessible too

If the area was not carpeted, such as a cupboard, you would still need a loose board that was marked with a durable notice indicating the joint. And it still wouldn't be great.
That's my opinion
 
Had a problem with this recently. Re-wired a priests house where he didn't want the walls chased to replace the old t&e switch drops. Trunking was also not an option so the only solution was to IR test the switch cables and extend them under the floors using MF hager boxes as they had been jb'd before in a right mess. I then placed a plan inside the fusebox identifying where they were located. Not ideal on a rewire but complied all the same.
 