I am doing a job at the moment and the plumber is wanting to put in a 14.4kw, and 2 x 3kw elements in a water cylinder.
plus there will be an electric cooker and other appliances. I am planning to put in a separate cu for the water heater... But concerned about the KW I may be pulling through... Any ideas would be much appreciated....
 
must be some super sized water cylinder .. Possibly having 20.4KW of heating elements. . . Can't see them all being on load at same time..
 
........Can't see them all being on load at same time..
I think it's fairly likely / almost certain it will draw full load when switched on from cold and during high water use periods. I'd run a supply large enough to accommodate the full 20.4 kW.
 
14.4kW heater? what's it for, a bloody swimming pool?
 
Is that a Fusion system boiler for electric wet CH, by any chance?
To misquote Marvo:
It will draw full load when switched on from cold... What are your concerns?
 
if the supply is on a 60A fuse, don't use it at the same time as the shower.
 
I am doing a job at the moment and the plumber is wanting to put in a 14.4kw, and 2 x 3kw elements in a water cylinder.
plus there will be an electric cooker and other appliances. I am planning to put in a separate cu for the water heater... But concerned about the KW I may be pulling through... Any ideas would be much appreciated....