so it's an old model -wonder if it came pre-wired at all?


looks like the lead+plug and final circuit are undersized then

also you'd need to check the suitability of supply and sub-main for SP welder


i would prob try welder at sub-board

as you might still be underpowered even with new final circuit


it'll be simpler if all existing loads are SP rather than 3P
 
Last edited by a moderator:
Along time ago I tried using my SP SIP 105 mig to weld a friends narrowboat. On the canal bank, on an extension lead about 50 M from the plug (on the canal side).

As you can imagine, it was like as much use as platting fog
 
Dave, there is no sub board. Its a small unit on an industrial estate, 3Phase supply - TNCS going straight into 3 phase Schneider DB.

SiP said the welder uses 30A constantly on max power, but can draw a peak 40A for a very small amount of time on initial start-up, would a type C/D curve 32A MCB allow for this, that way i can use a 4/6mm SWA and use 32A socket and plug without exceeding the rating of them.

What a pain in the arse this job has turned into! Started with... "can you just wire a 16A socket in for me"
 
ok sorry i though it was a shed or something

i'd prob test it at board on D type mcb, see if it's working properly and then size final circuit if all goes well

volt drop shouldn't be an issue on IND unit if there's spare capacity on a phase
 
Last edited by a moderator:
Along time ago I tried using my SP SIP 105 mig to weld a friends narrowboat. On the canal bank, on an extension lead about 50 M from the plug (on the canal side).

As you can imagine, it was like as much use as platting fog

i'm hoping to learn how to weld soon:yesnod:-never got round to it
 
It's bl00dy brilliant fun.

Although the welds can hurt as you look at the drip metal on your arm, and then 3 seconds later realise its working its way through your arm like chernobyl is working its way through the earth on its way to china
 
ok sorry i though it was a shed or something

i'd prob test it at board on D type mcb, see if it's working properly and then size final circuit if all goes well

volt drop shouldn't be an issue on IND unit if there's spare capacity on a phase

How do you mean 'test it at the board on a D type MCB'? Wire the welder flex into the DB on the 32A MCB and check it doesnt trip?
Can you get 4mm flex?

The board is literally empty, 1x Ring main, 1x Water heater, 1x Lighting circuit
 
Last edited by a moderator:
I’m about to buy a Stahlwerk CTM-250ST.
I contacted them about a note on website regarding residential use and electromagnetic interference. Their clarification was with regard to public low power supplies and danger for people with pacemakers. I also asked about electrical supply suggesting 32A/40A Type C MCB ON 220/240 circuit. Their response was: “ I need a 16A socket outlet and 16A Type C
 

Reply to Welder taking out MCB in the Canada area at ElectriciansForums.net

Similar Threads

Got an EICR testing to do on a site soon. Some was done 2018, some 2014... but their office cant find the reports... So got to start from scratch...
Replies
63
Views
7K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock