right slightly miffed tbh,
a friend has asked me to have a look at his mums board possibly to change, so i go start poking about (as you do).
got a tns with a old earth trip, a lead off the sheath of the incoming going to a met. nothing coming out of the met. an earth comes out of the earth trip and straight through the wall to next door, assuming its been piggy backed.
anyway a niceic (approved installer - not that, that means **** theses days) installed some heating wiring, and upgraded he earthing and bonding, a nice test sheet as well........... put a rod in the garden bonded water and oil to that, nothing else, put of the test sheet that its a tt system, and no rcd protection, even tho he's rewired some of the heating, altho i cant be 100% on what he's done.
with all this wrong im slightly miffed as you can guess, anyway the customer does not want to pay for this to be put right, understandably as it was done less than a year ago!
where to go from here?
 
Last edited by a moderator:
The customer MUST contact the contractor with the threat of an official complaint to the NICEIC if his work is not compliant.

Are you saying he bonded water and oil services straight to the earth electrode?

Are you looking at a voltage operated earth leakage device or an old BS4293 RCD? This is important as the former does not comply and should be replaced.
 
yes he bonded the oil and water straight to a earth electrode,
heres a picture of the trip
http://i11.tinypic.com/4byn435.jpg
cheers iq!

That's a voltage operated earth leakage circuit breaker, it is non-compliant and should be replaced although if the system is a TN-S you will not need to assuming you do the CU change.

The rod he installed (why on a TN-S?) should have gone to a main earth terminal with all protective bonding conductors emanating from that.

542.4.1 In every installation, a main earthing terminal shall be provided to connect the following to the earthing conductor:

The cpc's

The protective bonding conductors

Functional earths

LPC's
 
these are all questions that are baffling me, just wondering should i do anything before the nic has been informed, incase they want to see?
cheers again
danny
 
its almost like he's gone i cant be ***** to go all the way back to the met, i bang in a rod that'll do!
 
these are all questions that are baffling me, just wondering should i do anything before the nic has been informed, incase they want to see?
cheers again
danny

Well I would contact the contractor with a view to him rectifying his work before involving the NICEIC (if he is indeed a bona fide member).

Get a few photo's of the items you've described, before anyone does any further works.
 
will try and get hold of him, not sure he is going to be interested as he's in grimsby and my client is in oxford so miles away, not to sure how he got the job tbh.
cheers
danny
( will get some photos and post!)
 