Apologies but if no discrimination was given!?

In this case and, in your experience, which one would trip?

Many thanks.

Albert

99.9% of the time the one in the house. You need to consider what exactly the RCD is doing.

i.e. the house could have a cumulative leakage of 18mA and the garage almost none - introduce a fault at the garage and as most RCD's trip at around 24mA, the one in the house will trip first
 
No and No

So you would remove the 30mA protection from the house? I don't think so.

Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert
 
99.9% of the time the one in the house. You need to consider what exactly the RCD is doing.

i.e. the house could have a cumulative leakage of 18mA and the garage almost none - introduce a fault at the garage and as most RCD's trip at around 24mA, the one in the house will trip first

Makes sense.

Thank you.

Always learning.
 
Why do you want a 30ma time delay RCD? The 30ma rcd in the house will provide the protection to the sub cable and the circuits on the garage board.

Because the garage is also protected with a 30mA RCD thus giving no discrimination?!

Still, please do correct me if I am wrong.

Many thanks.

Albert
 
Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert

Where two, or more, RCDs are connected in series, discrimination must be provided, if necessary, to prevent danger (Regulation 531-02-09 refers). During a fault, discrimination will be achieved when the device electrically nearest to the fault operates and does not affect other upstream devices.
Discrimination will be achieved when ‘S’ (Selective) types are used in conjunction with downstream general type RCDs. The ‘S’ type has a built-in time delay and provides discrimination by simply ignoring the fault for a set period of time allowing more sensitive downstream devices to operate and remove the fault.
For example, when two RCDs are connected in series, to provide discrimination, the first RCD should be an ‘S’ type. RCDs with built in time delays should not be used to provide personal protection.
 
Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert

Just remember don't put 2 x 30mA RCD's on the same "circuits". Its that simple.
 
No discrimination as both are 30ma. What cable is supplying the garage? And what's the installation method? The RCD doesn't provide over current protection that's what the MCB is for.

I believe he's using 6mm T&E on clip direct method so (46A not taking into account any volt drop, still I believe it is a very short run, under 10 meters if that) method C if I am not mistaken.
 
Where two, or more, RCDs are connected in series, discrimination must be provided, if necessary, to prevent danger (Regulation 531-02-09 refers). During a fault, discrimination will be achieved when the device electrically nearest to the fault operates and does not affect other upstream devices.
Discrimination will be achieved when ‘S’ (Selective) types are used in conjunction with downstream general type RCDs. The ‘S’ type has a built-in time delay and provides discrimination by simply ignoring the fault for a set period of time allowing more sensitive downstream devices to operate and remove the fault.
For example, when two RCDs are connected in series, to provide discrimination, the first RCD should be an ‘S’ type. RCDs with built in time delays should not be used to provide personal protection.

I did wonder that and I was correct.
 
I thought he was in the process of doing this installation? The RCD in house will provide all the protection needed to sub cable and circuits so you don't need RCD at sub board end. The other option is, if there is room on main switch side of board or high integrity etc you could install an mcb on this side, select a suitable cable or installation method that doesn't require RCD protection and put a sub board in with an RCD at the garage end to give protection to the circuits.
 
I thought he was in the process of doing this installation? The RCD in house will provide all the protection needed to sub cable and circuits so you don't need RCD at sub board end. The other option is, if there is room on main switch side of board or high integrity etc you could install an mcb on this side, select a suitable cable or installation method that doesn't require RCD protection and put a sub board in with an RCD at the garage end to give protection to the circuits.

I think you've given the "friend" too much to think about.
 
I understand what you are saying.

However, people wouldn't be too happy to, in case of tripping, having to leave the garage to switch the RCD back on.

In my understanding (still studying) I'd rather have RCD at the garage.

Thanks.

Albert

Thats right Albert it would be better to have the RCD in the 'garage/shed', but if you also have one in the CU (in series) then there really is no point in having one in the shed as well due to the lack of dicrimination that you've already mentioned.

I think Murdochs point was that they shouldn't be 'called' garage/shed CU's as then people automatically fit them for sheds even if they have an RCD in the house that protects the garage circuit. 'People' could then just make a professional judgement whether or not an RCD is required in the shed, although it should be getting fitted by an electrician so they would know that a second RCD is not required.

Perhaps run cable from main CU without RCD protection (using correct methods/cable/route) and then have an RCD in the garage?
 
Last edited:
which brings us slightly off topic, to caravans, the touring type. a 30mA RCD must be provided at the hook-up point ( or upstream of it) to give protection to the hook-up cable. caravans themselves are fitted with 30mA RCDs. so. no discrimination between the 2. lesser of 2 evils.
 
which brings us slightly off topic, to caravans, the touring type. a 30mA RCD must be provided at the hook-up point ( or upstream of it) to give protection to the hook-up cable. caravans themselves are fitted with 30mA RCDs. so. no discrimination between the 2. lesser of 2 evils.

BUT.... the caravan is normally quite close the supply point, whereas the out building could be 100m away or further.

Caravans are a completely different can of worms
 
yeah, i know. just had to convert a site to TT where all the hook-ups were PME, with no earth connection to the SWA armour.
 
Last edited:
Two non time delayed RCDs in series will not have discrimination.
Certainly not if they are the same rating.
Even different rated (30/100/300/500) RCDs will not discriminate in most cases, remember that the RCD is coping with a potential fault current of at least 100's of amps so a difference of 0.47A is not going to make a difference.
Time delayed is the only way to ensure discrimination.

It must be noted here, if the garage supply cable requires rcd protection then a time delayed upfront rcd is not an option and will be in breach of regulations... everything you say is correct but without the point I'm making it could give a false impression to the OP that this is a solution...:)
 