he's talking out of his arse. the 63A and 40A ratings are just the max. operating load of the RCDs. it's the 30mA rasting that does not give discrimination. you're right.
LOL...
He really was OMG!
I just came from his house and have advised him to stop.
There is no 63A 30mA in the house consumer unit.
In fact, the consumer unit is an old rewirable fuse board.
5A - 5A - 15A - 30A - 30A - 30A
5A (1.0mm x 2) = Not a clue as to what circuits it's protecting.
5A (1.00mm x 2) = It's protecting both downstairs and upstairs lighting circuits
15A (2.5mm x 1) = Immersion Heater
30A (2.5mm x 4) = Both down and upstairs ring main.
30A (2.5mm x 3) = From what I could gather, it seems this is serving 2 radial circuits + the garage (the one being worked on with a so called garage consumer unit)
30A (4.00mm X 1 & 2.5mm x 1) = Cooker + second garage. (Detached from the house, about 20 meters of cable supplying only a fluorescent tube.)
My advice to him was to not go ahead with the garage upgrade and think about upgrading the main consumer unit to start with. Also, if he does go ahead with upgrading the main C.U. to either have the detached garage on SWA cable or limit it by fitting a 6A MCB which should be RSD protected. This would however not allow for future upgrade of the garage should he require the installations of sockets.
Many thanks to all.
Regards,
Albert