Carlos Arruda

Hi all.

I am finishing my level 3 in electrical installations and as such, I have tried to explain this to a friend.

So much so, that now he's got me doubting myself.

He's powering his garage which is attached to the main house.

He's also providing the circuit supplying the garage with RCD protection.

At the garage consumer unit, he's got a standard 40A RCD 30mA protecting a 32A type B and 6A type B MCBs.

My advise for him was in terms of the given protection to the both circuits in the garage and the circuit from the main consumer unit to the garage. He's not providing discrimination as both RCDs are rated at 30mA.

Now, he's adamant that discrimination has been given as one RCD is 63A and the other is 40A.

Am I wrong when I say that discrimination hasn't been given.

Kind regards.

Albert
 
he's talking out of his arse. the 63A and 40A ratings are just the max. operating load of the RCDs. it's the 30mA rasting that does not give discrimination. you're right.
 
Two RCDs on The same supply, not a good idea, no discrimination unless the one in the house is a time delay, or a different mA rating ie CU house 100mA and Garage 30mA
 
get him to perform a RCD test in the garage and see which RCD trips.
 
Two non time delayed RCDs in series will not have discrimination.
Certainly not if they are the same rating.
Even different rated (30/100/300/500) RCDs will not discriminate in most cases, remember that the RCD is coping with a potential fault current of at least 100's of amps so a difference of 0.47A is not going to make a difference.
Time delayed is the only way to ensure discrimination.
 
Last edited:
If sheds stopped just stocking "garage" CU's which all have RCD's in, this confusion would end.

People think the garage needs a RCD irrespective of whether or not the house has one too!
 
Two RCDs on The same supply, not a good idea, no discrimination unless the one in the house is a time delay, or a different mA rating ie CU house 100mA and Garage 30mA

Hi Pete999.

There has been several discussions on forums about the use of two RCDs on the same supply.

I even took this subject to college and, unless I was sleeping throughout the lesson, it seems that it's the regulations?

But still, to my understanding, the RCD on the main consumer unit provides additional protection to the cable supplying the garage and the RCD in the garage is providing additional protection to the garage circuits i.e light and sockets.

On another note to all, is any RCD rated at above 30mA considered to be additional protection? I was under the impression that additional protection is only given at 30mA! I might be wrong.

I have also been looking online today for 30mA time delayed RCD and couldn't find any at this rating.

Many thanks for clearing my main question.

He won't be happy.

Cheers,
Albert
 
If sheds stopped just stocking "garage" CU's which all have RCD's in, this confusion would end.

People think the garage needs a RCD irrespective of whether or not the house has one too!

I understand what you are saying.

However, people wouldn't be too happy to, in case of tripping, having to leave the garage to switch the RCD back on.

In my understanding (still studying) I'd rather have RCD at the garage.

Thanks.

Albert
 
Hi Pete999.

There has been several discussions on forums about the use of two RCDs on the same supply.

I even took this subject to college and, unless I was sleeping throughout the lesson, it seems that it's the regulations?

But still, to my understanding, the RCD on the main consumer unit provides additional protection to the cable supplying the garage and the RCD in the garage is providing additional protection to the garage circuits i.e light and sockets.

On another note to all, is any RCD rated at above 30mA considered to be additional protection? I was under the impression that additional protection is only given at 30mA! I might be wrong.

I have also been looking online today for 30mA time delayed RCD and couldn't find any at this rating.

Many thanks for clearing my main question.

He won't be happy.

Cheers,
Albert

No and No

So you would remove the 30mA protection from the house? I don't think so.
 
Last edited by a moderator:
Apologies but if no discrimination was given!?

In this case and, in your experience, which one would trip?

Many thanks.

Albert

99.9% of the time the one in the house. You need to consider what exactly the RCD is doing.

i.e. the house could have a cumulative leakage of 18mA and the garage almost none - introduce a fault at the garage and as most RCD's trip at around 24mA, the one in the house will trip first
 
No and No

So you would remove the 30mA protection from the house? I don't think so.

Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert
 
99.9% of the time the one in the house. You need to consider what exactly the RCD is doing.

i.e. the house could have a cumulative leakage of 18mA and the garage almost none - introduce a fault at the garage and as most RCD's trip at around 24mA, the one in the house will trip first

Makes sense.

Thank you.

Always learning.
 
Why do you want a 30ma time delay RCD? The 30ma rcd in the house will provide the protection to the sub cable and the circuits on the garage board.

Because the garage is also protected with a 30mA RCD thus giving no discrimination?!

Still, please do correct me if I am wrong.

Many thanks.

Albert
 
Murdoch;

That is the issue when so many say two RCDs in the same circuit is not a good idea.

I don't see this as two RCDs in the same circuit.

I wouldn't remove the one in the house main consumer unit as this RCD is the one giving additional protection to the circuit supplying the garage.

And it's my understanding that the other RCD in the garage is giving additional protection to the garage circuits.

I think I see where the issue is with these so called garage C.U. The lack of a dual pool isolating switch. This would then separate both RCDs.

But please, do correct me if I am wrong.

One is always learning and I would just like to give my friend the best correct advice.

Thank you.

Albert

Where two, or more, RCDs are connected in series, discrimination must be provided, if necessary, to prevent danger (Regulation 531-02-09 refers). During a fault, discrimination will be achieved when the device electrically nearest to the fault operates and does not affect other upstream devices.
Discrimination will be achieved when ‘S’ (Selective) types are used in conjunction with downstream general type RCDs. The ‘S’ type has a built-in time delay and provides discrimination by simply ignoring the fault for a set period of time allowing more sensitive downstream devices to operate and remove the fault.
For example, when two RCDs are connected in series, to provide discrimination, the first RCD should be an ‘S’ type. RCDs with built in time delays should not be used to provide personal protection.
 

Reply to What does provide discrimination? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
371
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock