Hi all.

I am finishing my level 3 in electrical installations and as such, I have tried to explain this to a friend.

So much so, that now he's got me doubting myself.

He's powering his garage which is attached to the main house.

He's also providing the circuit supplying the garage with RCD protection.

At the garage consumer unit, he's got a standard 40A RCD 30mA protecting a 32A type B and 6A type B MCBs.

My advise for him was in terms of the given protection to the both circuits in the garage and the circuit from the main consumer unit to the garage. He's not providing discrimination as both RCDs are rated at 30mA.

Now, he's adamant that discrimination has been given as one RCD is 63A and the other is 40A.

Am I wrong when I say that discrimination hasn't been given.

Kind regards.

Albert
 
he's talking out of his arse. the 63A and 40A ratings are just the max. operating load of the RCDs. it's the 30mA rasting that does not give discrimination. you're right.
 
Two RCDs on The same supply, not a good idea, no discrimination unless the one in the house is a time delay, or a different mA rating ie CU house 100mA and Garage 30mA
 
get him to perform a RCD test in the garage and see which RCD trips.
 
Two non time delayed RCDs in series will not have discrimination.
Certainly not if they are the same rating.
Even different rated (30/100/300/500) RCDs will not discriminate in most cases, remember that the RCD is coping with a potential fault current of at least 100's of amps so a difference of 0.47A is not going to make a difference.
Time delayed is the only way to ensure discrimination.
 
Last edited:
If sheds stopped just stocking "garage" CU's which all have RCD's in, this confusion would end.

People think the garage needs a RCD irrespective of whether or not the house has one too!
 
Two RCDs on The same supply, not a good idea, no discrimination unless the one in the house is a time delay, or a different mA rating ie CU house 100mA and Garage 30mA

Hi Pete999.

There has been several discussions on forums about the use of two RCDs on the same supply.

I even took this subject to college and, unless I was sleeping throughout the lesson, it seems that it's the regulations?

But still, to my understanding, the RCD on the main consumer unit provides additional protection to the cable supplying the garage and the RCD in the garage is providing additional protection to the garage circuits i.e light and sockets.

On another note to all, is any RCD rated at above 30mA considered to be additional protection? I was under the impression that additional protection is only given at 30mA! I might be wrong.

I have also been looking online today for 30mA time delayed RCD and couldn't find any at this rating.

Many thanks for clearing my main question.

He won't be happy.

Cheers,
Albert
 

Reply to What does provide discrimination? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
266
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
409
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock