It must be noted here, if the garage supply cable requires rcd protection then a time delayed upfront rcd is not an option and will be in breach of regulations... everything you say is correct but without the point I'm making it could give a false impression to the OP that this is a solution...:)
Yup, and thats why we all need to very careful dishing out advice to all and sundry.
he's talking out of his arse. the 63A and 40A ratings are just the max. operating load of the RCDs. it's the 30mA rasting that does not give discrimination. you're right.
LOL...
He really was OMG!
I just came from his house and have advised him to stop.
There is no 63A 30mA in the house consumer unit.
In fact, the consumer unit is an old rewirable fuse board.
5A - 5A - 15A - 30A - 30A - 30A
5A (1.0mm x 2) = Not a clue as to what circuits it's protecting.
5A (1.00mm x 2) = It's protecting both downstairs and upstairs lighting circuits
15A (2.5mm x 1) = Immersion Heater
30A (2.5mm x 4) = Both down and upstairs ring main.
30A (2.5mm x 3) = From what I could gather, it seems this is serving 2 radial circuits + the garage (the one being worked on with a so called garage consumer unit)
30A (4.00mm X 1 & 2.5mm x 1) = Cooker + second garage. (Detached from the house, about 20 meters of cable supplying only a fluorescent tube.)
My advice to him was to not go ahead with the garage upgrade and think about upgrading the main consumer unit to start with. Also, if he does go ahead with upgrading the main C.U. to either have the detached garage on SWA cable or limit it by fitting a 6A MCB which should be RSD protected. This would however not allow for future upgrade of the garage should he require the installations of sockets.
Many thanks to all.
Regards,
Albert
LOL...
He really was OMG!
Many thanks to all.
Regards,
Albert
Why????
I see where you are coming from Dillb.
It's just I got so annoyed with him as he clearly has no clue to what he's doing and mislead me to believe he had a split load dual RCD consumer unit. Perhaps my own assumption was my greatest enemy here. Oh well!
I guess he could always go ahead and have at least the garage circuits RCD protected.
what is needed is a hi-integrity CU. either RCBO or a dual RCD board with 1-3 non-RCD ways. SWA to garage/s siutably sizedand MCB protected for the load (not forgetting volt drop) from a non-RCD way. that's his starter for 10. let him think about how to gland and terminate the SWA so as to comply.
Tbh I think you and he need to get a sparky involved
Solution;
Tell him to go to big Orange shed
Buy RCD garage unit.
Ask person roaming the aisles what size and length of cable it needs.
Go to checkouts.. Sorted.
No fear of any blame being attached to anyone other than the Shed and himself.
Solution;
You are absolutely right.
I now somehow feel responsible as I know what's in place and to an extent, what needs to be done.
It's a position I don't like to be in and I hate to let a good friend down.
if your mate is a qualified spark, he should knowe how to do it. if not, the best advice you can give him is to employ one. don't get too involved or it may come back to bite your arse when he makes a bollox of it.
Mind your language or ye'll be gettin a -------ing off the Gaffer!! ;)
This is the same guy that you previously said was allowing you to change his CU for training purposes, and you would be supervised by your college tutor? Why is he now getting involved in the work? Is he an electrician? Confused
Carlos Arruda,