marcuswareham

Esteemed
Arms
Reaction score
199
The situation is:

Power is needed inside a greenhouse to power a specialized greenhouse heater, a timed motorized window opener and a light. The lights can be double insulated but the heater and windows device are both class 1.

The greenhouse has a metal frame that is in good contact with soil and the floor inside the greenhouse is a mix of soil and paving slabs

The house is TN-C-S

I originally thought making the greenhouse TT would be the best option but there is an issue with that because the house supply cable and a metal water pipe run close to one side of the greenhouse (about 1.5m away) so there is no available location to put in an earth rod with enough separation distance from the water pipe which is at PME earth potential

If the TN-C-S earth was used in the greenhouse then the metal frame of the greenhouse would have to be bonded with 10mm although this makes the risk of the greenhouse metalwork and the heater being at a dangerously high voltage in a PEN fault with anyone inside or just outside of the greenhouse in good contact with true earth (and the metal frame is likely to be touched (each time door is opened))

So In this case I am not sure using the TN-C-S earth and bonding the frame is a good option either, I was thinking also perhaps a matt:e or viridian pen fault devices could work but the problem would be that this box would only isolate the L,N & CPC but not the 10mm bonding conductor so renders it pointless as the greenhouse frame would remain connected to PME, these are also deigned for EV charging and there is no way the greenhouse sockets could reasonably be expected to be used to charge a vehicle as stated in 722.411.4.1

I imagine an isolation transformer would cost mega money (demand is around 2kw)

Thanks
 

Reply to What earthing arrangement would you use in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi All, I understand the requirement for PEN fault detection on EV chargers for TN-C-S installs (or to place an earth rod). However, when I was...
Replies
3
Views
1K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
571
A friend of the family recently lost her husband to the big C so I need to be careful. Every small thing is sending her into tears so when her...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock