Ioz, that makes it very understandable. Cheers.Table 52.2 - cable surrounded by thermal insulation:
Length in insulation 50mm derate cable by 0.88.
Length in insulation 100mm derate cable by 0.78.
Length in insulation 200mm derate cable by 0.63.
Length in insulation 400mm derate cable by 0.51.
So a cable normally capable of carrying 47 amps clipped direct is reduced to 41 amps for 50mm of insulation.
And 36 amps for 100mm.
And 29 amps for 200mm.
And 23 amps for 400mm.
These are some of the calculations that need to be made when designing a circuit.
These are also the calculations that all too often are not made when designing a circuit.
Having said that, your shower may well be fine and not cause any problems. But there is always an associated risk when shortcuts are taken.
Paul