Are the showersgenerally getting more powerful? I seem to remember a year or two ago all the shower threads involved 9kW supplies...
 
Yes 10.5- 10.8kW now seem to be a popular choice Marvo - the perception being that you'll get better flow of hot water even in winter when the incoming water is very cold. But the customers [and often plumbers] don't understand the electrical implications at all unfortunately.
 
Wow, 10.8kW is quite something on a single phase domestic supply. If they keep getting larger you're going to be terminating 16mm wiring into one of those rediculous ceiling mounted pull switches pretty soon.:sweatsmile: I'd pay good money to watch a sparky doing that.:p
 
From my 2002 MK catalogue s.p solid neutral RCBO's only up to 45A.
Do you still have off-peak heating?
 
With that board I'd go with a separate unit for the shower. You can get electric showers up to 12.5KW which is pushing things rather a lot. We fitted one last year (with permission from DNO) wired with 16mm T+E. Ridiculous.
 
With that board I'd go with a separate unit for the shower. You can get electric showers up to 12.5K.
I wish that I had suggested that, oh I did!
Keep the existing fuseboard and add a separate 'mini' CU that has an RCD and an MCB in it (aka shower unit)
Or is that not what you are looking for?
CPSP2.JPG
 