You won’t even get a 50A MCB for that board!
10.8 KWwhat wattage is the shower?
All is in placeWith that age of CU , wonder what the earthing and bonding is like?
10.8 KW

I wish that I had suggested that, oh I did!With that board I'd go with a separate unit for the shower. You can get electric showers up to 12.5K.
Keep the existing fuseboard and add a separate 'mini' CU that has an RCD and an MCB in it (aka shower unit)
Or is that not what you are looking for?
![]()